The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
2 registered (HotLine1, Lostazhell), 46 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#2225 - 06/28/01 01:01 PM Existing range and Dryer 3-wire circuits
C.Urch Offline

Registered: 05/23/01
Posts: 36
Loc: Kill Devil Hills, NC USA
Can someone give me code references or insight regarding service changes and how they affect existing range and dryer circuits. I'm upgrading an old 3 wire service to a 200 amp (disconnect feeding a main lug panel) 4-wire and am wondering if I need to install new 4 wire range and dryer circuits. This is an old flat top cinder block bungalow and needless to say, major destruction work would be required.

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#2226 - 06/28/01 02:51 PM Re: Existing range and Dryer 3-wire circuits
Mike Offline

Registered: 02/21/01
Posts: 65
I will venture to say that you shouldn't have to upgrade the 3-wire range and dryer circuits. But, the ultimate decision belongs to the AHJ.

[This message has been edited by Mike (edited 06-28-2001).]

#2227 - 06/28/01 03:54 PM Re: Existing range and Dryer 3-wire circuits
Tom Offline

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
This may be up to your AHJ, but as I stated on another board, I think you should replace the cables & outlets or purchase service entrance equipment that has room for a couple of more 2 pole breakers & extend the 3 wire cables into the new service entrance box.

Although three wire feeds were allowed for these types of loads, they were not allowed to be fed from a sub-panel, which is what you will be doing when you upgrade the service.

The current requirement is 250-140(3). The old reference was 250-60(c).


[This message has been edited by Tom (edited 06-28-2001).]
Few things are harder to put up with than the annoyance of a good example.

#2228 - 06/28/01 04:13 PM Re: Existing range and Dryer 3-wire circuits
sparky Offline

Registered: 10/18/00
Posts: 5545
I will always try to include a 3 to 4 wire upgrade in such a service change, however if we would like to delve into the NEC:

250-140's key word is 'existing'

250-142(b) EX #1 states;
The frames of ranges, wall mounted oven, counter-mounted cooking units, and clothes dryers under the conditions permitted for existing installations by Section 250-140 shall be permitted to be grounded by a grounded conductor

Ok, so tape that puppy up & off to the N-bar!


90-5(b) Permissive Rules
nice if you do it, but don't gotta!

Ok, so on to the G-bar???


Art 100, Special Permission;
basically what Tom said

So can we do a poll of AHJ's here?
Door #1--Noodle Bar
Door #2--G-bar
Door #3--rejected until a 4-wire set-up

[This message has been edited by sparky (edited 06-28-2001).]

#2229 - 06/29/01 10:55 AM Re: Existing range and Dryer 3-wire circuits
silverbk Offline

Registered: 02/24/01
Posts: 61
I would use the neutral bus, because a dryer and a range use the grounded conducter for several 120 volt circuits within the unit. For the timers and lighting. I would never intentionally put current onto a ground detail.

#2230 - 06/29/01 12:23 PM Re: Existing range and Dryer 3-wire circuits

If the connection is in the main panel were neutral and ground are bonded, I don't see a difference between doors 1 and 2. Since it is carrying current, I would treat it as a neutral. Door 3 is the safe way.

#2231 - 07/04/01 06:02 AM Re: Existing range and Dryer 3-wire circuits
RickG Offline

Registered: 07/04/01
Posts: 37
Loc: South County, R.I. USA
I am with silverbk, the neutral/ground MUST go to the neutral buss.