The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Live Chat Feature
by Trumpy
01/20/17 06:20 PM
Safety at heights?
by gfretwell
01/19/17 07:16 PM
failed home inspection.
by gfretwell
01/19/17 07:03 PM
Webmaster > Admin
by Admin
01/19/17 05:49 PM
Old Bath Fan
by gfretwell
01/19/17 01:38 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Admin 33
HotLine1 20
Ruben Rocha 17
Trumpy 15
gfretwell 15
Who's Online
1 registered (Admin), 0 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#22036 - 02/17/03 04:49 AM Salt Water Rated?
tsolanto Offline
Member

Registered: 09/03/02
Posts: 131
Loc: Long Island NY
I spent half Saturday and all day Sunday troubleshooting and temporarily repairing a problem with a service feeder.

Who's got it better than me?

The electrician that did the wiring for this apartment complex put all the meters in one of two buildings. All the feeders for the second building were run underground to each apartment load center.

The tenant was complaining that the power would go out in the whole apartment ramdomly. I met with the building super and found that the main for that particular apartment was tripping. I tested everything I could think of and found that the wiring going from the building with the main to the other building had a high impedence short from phase a to ground. From time to time it would trip the apartment main.

These apartments are 100yds. from the open bay. The conductors used to feed underground had markings on it (Type HH). I probably can assume this is RHH but it did not say it on the wire.

Question is... Can HH or RHH handle the rigors of contact with salt water. Is that what caused this problem? Maybe a Knick in the wire in conjuction with the salt caused the problem? We won't know until it gets dug up but I was wondering if RHH could handle salt?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#22037 - 02/17/03 05:07 AM Re: Salt Water Rated?
electure Offline


Member

Registered: 12/24/00
Posts: 4229
Loc: Fullerton, CA USA
Any underground run is considered a wet location, and the conductors must be rated as such.
Type RH or RHH is for dry locations only. Type RHW is rated for wet locations...S