The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by ghost307
Today at 06:25 AM
International Wire Colour Codes
by Tjia1981
Yesterday at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 229 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#21984 - 02/14/03 11:21 AM netural and hot reversed?
rayh78 Offline

Registered: 11/11/01
Posts: 26
Used one of the little plug in testers. Test ok on the first outlet of a kitchen circut. the 2nd outlet box shows reversed. Switched white & black wires at outlet and still shows reversed. This should have at least given proper reading. Outlets are ground wire connected and white to large prong opening as required. Very confused?
Also is the only way to test bare cable for hot/netural is to have to connect to a outlet first in order to use a plug in tester. Dosnt seem to be a way with my fluke.
Thanks for any suggestions

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#21985 - 02/14/03 12:09 PM Re: netural and hot reversed?
JCooper Offline

Registered: 12/30/02
Posts: 229
Loc: Kendall Park, NJ USA
You can use your fluke, put one probe in ground and the other in neutral, should be 0 volts and 0, or close maybe 5 or 10, ohms. Netx probe between neutral and hot, verify voltage, and again between hot and ground.

#21986 - 02/14/03 01:48 PM Re: netural and hot reversed?
rayh78 Offline

Registered: 11/11/01
Posts: 26
Thanks for info on reading fluke.

any idea why it did not work to switch black and white wires on outlet to get a good reading?

#21987 - 02/14/03 02:09 PM Re: netural and hot reversed?
txsparky Offline

Registered: 05/25/01
Posts: 578
Loc: Magnolia,.Texas U.S.A.
It's not reversed wiring. If you unplug everything on this circuit, and turn off all switches, your tester will correctly read "open neutral". Somewhere on this circuit, the white wire has become disconnected. This usually happens when a backstab of the white wire becomes loose. You may need to open up every box on the circuit (working or not) and move backstabbed connections to adjacent screws. While you're in there, tighten up any wire nuts. Start with the non-working boxes, and then move to the closest working boxes on the same circuit.

#21988 - 02/15/03 05:28 PM Re: netural and hot reversed?
Trumpy Offline


Registered: 07/05/02
Posts: 8532
Loc: SI,New Zealand
Good Call, mate, would have said the same thing.
Let's face it, these days if you're not young, you're old - Red Green grin