#2192 - 06/25/01 07:08 AM 4-20ma signal
frank Offline
Member
Registered: 05/29/01
Posts: 374
Loc: windsor ontario canada
a 4-20ma signal,500psi to 1250psi.at 7ma i was told you will get 640.625.whats the formula for this ratio thanks
Top
Work Gear for Electricians and the Trades
#2193 - 06/25/01 08:25 AM Re: 4-20ma signal
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
4mA = 500 psi 20 mA = 1250 psi.
4-20 ma is the span 16 mA is the range
500 - 1250 psi is the span 750 is the range
7ma - 4mA = 3mA 3/16 is the % of range
3/16(750)= % of psi range = 140.625psi
Add the 140.625 to the minimumn span of 500 psi to get 640.625psi.

[(signal mA - 4) divided by 16] X (variable range) + variable minimum span

Don(resqcapt19)
_________________________
Don(resqcapt19)
Top
#2194 - 06/25/01 09:43 AM Re: 4-20ma signal
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Or...

750(engineering units span or range) divided by 16(signal span or range)= 46.875 PSI per mA.
3 x 46.875 = 140.625
140.625 + 500(zero value) = 640.625

conversely...
16 divided by 750 = .02133 Psi per mA
.02133 x 140.625 = 3mA
3mA + 4(live zero value)= 7mA
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 43 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals