The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
failed home inspection.
by HotLine1
17 minutes 20 seconds ago
Safety at heights?
by Trumpy
Today at 05:25 AM
Old Bath Fan
by gfretwell
Today at 01:38 AM
Search Function
by Webmaster
Yesterday at 11:13 PM
Forum Software Upgrade coming soon...
by Webmaster
Yesterday at 09:17 PM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 30
HotLine1 21
Ruben Rocha 16
Trumpy 13
gfretwell 13
Who's Online
2 registered (HotLine1, Webmaster), 0 Guests and 195 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#217828 - 12/01/16 11:10 PM Sprinklered equipment 26-008
bigpapa Offline
Member

Registered: 03/18/06
Posts: 77
Loc: canada
This rule says that electrical equipment rooms must have sprinkler drip shields on electrical equipment.

Does not say other rooms. Am I to assume that having a bit of water spray into panels is acceptable in other areas?

Top
2017 / 2014 NEC & Related Books and Study Guides
#217829 - 12/02/16 06:28 AM Re: Sprinklered equipment 26-008 [Re: bigpapa]
twh Offline
Member

Registered: 03/11/04
Posts: 899
Loc: Regina, Sask.
Appendix B explains that the problem is ventilated enclosures.

Top
#217830 - 12/02/16 04:24 PM Re: Sprinklered equipment 26-008 [Re: bigpapa]
bigpapa Offline
Member

Registered: 03/18/06
Posts: 77
Loc: canada
I spoke to the inspector having jurisdiction and he said that drip protection definitely required for electrical rooms as stated in the rules, but will also enforce in other areas if its possible for water to pool on top of the panel board.

In this case side entry allowed unless using connectors capable of greatly restricting the amount of water allowed in. Oddly a dry type EMT connector would be accepted for top entry, a flex connector not.

Gray area. Best to check first.

Top
#217906 - 01/02/17 10:44 AM Re: Sprinklered equipment 26-008 [Re: bigpapa]
frank Offline
Member

Registered: 05/29/01
Posts: 373
Loc: windsor ontario canada
I've been there.I would call him and see.He had no problem showing up and telling me what he wanted.The existing installations were allowed to exist as is.

Top