The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 137 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#217828 - 12/01/16 11:10 PM Sprinklered equipment 26-008
bigpapa Offline
Member

Registered: 03/18/06
Posts: 77
Loc: canada
This rule says that electrical equipment rooms must have sprinkler drip shields on electrical equipment.

Does not say other rooms. Am I to assume that having a bit of water spray into panels is acceptable in other areas?

Top
2014 / 2011 NEC & Related Books and Study Guides
#217829 - 12/02/16 06:28 AM Re: Sprinklered equipment 26-008 [Re: bigpapa]
twh Offline
Member

Registered: 03/11/04
Posts: 898
Loc: Regina, Sask.
Appendix B explains that the problem is ventilated enclosures.

Top
#217830 - 12/02/16 04:24 PM Re: Sprinklered equipment 26-008 [Re: bigpapa]
bigpapa Offline
Member

Registered: 03/18/06
Posts: 77
Loc: canada
I spoke to the inspector having jurisdiction and he said that drip protection definitely required for electrical rooms as stated in the rules, but will also enforce in other areas if its possible for water to pool on top of the panel board.

In this case side entry allowed unless using connectors capable of greatly restricting the amount of water allowed in. Oddly a dry type EMT connector would be accepted for top entry, a flex connector not.

Gray area. Best to check first.