#217432 - 07/30/16 06:37 PM Locked rotor, no burnout
poorboy Offline
Member
Registered: 06/02/05
Posts: 124
Loc: Central Maine
A small fractional HP pump stopped working in a customers little garden pond (she creates a 12 inch waterfall with it). The braided line from a duck decoy had been sucked into the intake(no filter)and wrapped around the impeller shaft and stopped the submerged motor cold for a couple days.

I took the cover off, removed the string, and reassembled it and it works fine.

What prevents this motor from overheating and shorting the windings?



Top
Work Gear for Electricians and the Trades
#217433 - 07/31/16 12:44 AM Re: Locked rotor, no burnout [Re: poorboy]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
My guess is liquid cooling and a fairly modest current draw in the first place. Is it "shaded pole"? They are pretty resilient in LR but you pay for it with virtually no starting torque.
_________________________
Greg Fretwell
Top
#217586 - 09/07/16 02:26 AM Re: Locked rotor, no burnout [Re: poorboy]
Entropy Offline
New Member
Registered: 09/05/16
Posts: 1
Loc: Washington
Definitely a problem with the liquid cooling.
_________________________
Semenax here http://www.danpeek.com/semenax-review-results
Top
#217648 - 09/29/16 01:18 PM Re: Locked rotor, no burnout [Re: poorboy]
jraef Offline
Member
Registered: 07/21/04
Posts: 93
Loc: San francisco, CA, USA
99% of those little pond pumps are cheap little shaded pole motors. They are "impedance limited" in terms of protection, meaning they don't need a fuse or breaker because they are inherently current limiting at their own rated current. So stopping the rotor is, to the motor, no different than running at full load, other than the fact that instead of moving water, it just heats it.
_________________________
JRaef
Top
#217654 - 09/30/16 04:48 AM Re: Locked rotor, no burnout [Re: poorboy]
andey Offline
Member
Registered: 08/05/08
Posts: 35
Loc: germany
It is not fully impossible for a shaded pole Motor to overheat, it depends on the size and design. See link.
Maybe, because the water pump manufacturer did a little thinking, they designed their motor expecting it to get stuck by obstacles once in a while.

http://www.electrical-forensics.com/BathroomFans/BathroomFans.html
Top
#217655 - 10/01/16 02:04 PM Re: Locked rotor, no burnout [Re: poorboy]
geoff in UK Offline
Member
Registered: 12/30/02
Posts: 179
Loc: UK
Interesting stuff Andey. I knew that those shaded pole motors could overheat, and burn out the windings even, but I hadn't seen them as such a fire risk. I would hope that the rising current as sections of winding shorted would blow a fuse or trip a breaker in most cases, but it certainly justifies the thermal fuses we often see now.

Regarding pond pumps, I've messed around with those and found that you can even pull the rotor in and out whilst it's energised with no discernable effect on the stator temperature. I agree with jraef that the winding impedance limits the current to a harmless level.
Top
#217668 - 10/06/16 05:50 PM Re: Locked rotor, no burnout [Re: poorboy]
jraef Offline
Member
Registered: 07/21/04
Posts: 93
Loc: San francisco, CA, USA
Not sure how old the fans were that he investigated, but i remember that thermal fuse wire being added back in the late 70s when I worked for a Nutone distributor. That issue was somewhat unique to SP motors used on vent fans, because it was implied that the fans would be moving air across them and keep them cool. Before adding the fuse link, the thought was that if you turned on a vent fan and it didn't vent the air, you investigated and fixed it. but people kept ignoring them and some caught on fire, so UL added the requirement for the fuse link, maybe around 1978? That issue would not likely happen in a pond pump surrounded by water. I had mine stop pumping and found out that my wife turned it on and left it on, for maybe 3 weeks before remembering to tell me about it. It just had a little stick in the impeller, I removed it and it started pumping again.
_________________________
JRaef
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6775
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 87 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals