12.5A through 0.75mm flex (just out of curiosity)
Over double what the British are willing to rate this size of cord for, and it still held together. (Although I wouldn't coil it up with this degree of loading...)
Image Details
Poster LongRunner Offline
Posted 07/14/16 09:24 PM
Description
I noted in my thread on power boards/strips (in the small text) that my calculations said "if 1.0mm flex can carry 16A under optimal conditions, then 0.75mm could even do about 13A in the same scenario":
  • 13A through 0.75mm flex - 10.5W/metre max. (2 load wires * 0.0267R/m at 20C * TCR 1.16 to 60C * 13A squared)
  • 16A through 1.0mm flex - 11.9W/metre max. (2 load wires * 0.02R/m at 20C * TCR 1.16 to 60C * 16A squared)
BTW, those resistance values are for tinned conductors, for bare conductors they're slightly less (0.026R and 0.0195R respectively).

Confirmed, apparently, with this arrangement (using two heaters with currents/power indicated in the overlay); I ran it for over an hour and the cords still stayed at a tolerable temperature (not too hot to touch, nor getting overly soft). Note the pillow (from my bed) in the background, which I added for 'good measure' cool. (On a side note, the IEC 60320 C13-C18 - rated for 10A, like the base version of AS/NZS 3112 - are also meant to survive testing to this current, from what I've read; and presumably the 16A C19-C24 are meant to survive 20A.)

This sure flies in the face of hyperbole from some (mainly British) sources about the 0.75mm versions of C13-C17 cords being "fire hazards", at least. (The short ones, anyway. Not that I would recommend going over 10A in normal use of these - although the UL/CSA are willing to rate the C13-C18 as high as 15A with 14AWG cordage, but I don't really trust that.) Even the connectors stayed fairly cool (although it should be noted that the 10A and 15A versions of AS/NZS3112 outlets and rewireable plugs/trailing sockets seem all-but-identical anyway apart from the earth pin width, the absence of a shroud on the majority of 15A trailing sockets, and maybe the contact sizing in the outlet switches).

The cord itself, in case you're wondering, was salvaged from an el-cheapo PC speaker set (a bit of an odd choice there, given that those are more usually Class II with a type H03VVH2-F cord; the earth wire was only connected to the transformer frame, and the cord was even squashed into a cord-grip meant for a flat cord!), and measures about 125cm 'net' so is within the '2m limit' for the 'downsized' cords. The plug is the original moulded part, the socket Deta model 6338 (which clamps the cord solidly enough - far better than the HPM versions I used in extension cords I assembled in years past). And it is ordinary-duty (H05VV-F), not light-duty (H03VV-F) (which so far as I know, isn't allowed for any normal extension cords here in Australia).

As an aside, I've noticed that a properly fitted (and in good condition) rewireable plug and trailing socket, mated together, seem to run almost supernaturally cool compared to most of the combinations of moulded-on versions that I've tested with the heaters (including their own plugs!). I presume that the moulded cordsets are manufactured with less stringent methods of terminating the wires to the pins/receptacles (although I'll admit that the common DIY pitfall of trapping the insulation in the terminals doesn't work out much better). (There's significant variance among them, too, so I'll probably be 'cherry-picking' from my stash of IEC 60320 cordsets to use with heavier loads - should I get any high-power appliance that has a C14 or C18 inlet on it in the first place...)
Dimensions 1024x768
Size 74.83 KB
UBBCode
Thumbnail
Medium
Full

Comments
#217778 - 11/19/16 05:04 PM Re: 12.5A through 0.75mm flex (just out of curiosity) [Re: LongRunner]
uksparx Offline
Member
Registered: 04/25/05
Posts: 44
Loc: Egremont,Cumbria,UK
I've noticed we are getting a lot of 3kW kettles here with smaller flex now. Admittedly, that flex is very short and the boil time is very quick, so I guess they reckon it's okay. It is interesting though, to see what flex will cope with, particularly as the Brits are so obsessed with having 3amp fuses in plugs for lamp flex etc. If it's so bad having less (i.e a 16 amp mcb) protection, why aren't there more fires all around the globe where they don't have this protection? Just a thought....
Top
Super Rod Cable Installation Tools

Super Rod Cable Rod System
Super Rod Cable Rod System -
Voted
Best Product of the Last 50 Years by members of NICEIC


Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 50 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals