The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
breaker meltdown
by sparky
Today at 07:30 PM
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 10
sparky66wv 8
gfretwell 8
Vlado 6
Who's Online
0 registered (), 286 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#217353 - 06/22/16 11:10 PM Outdoor transformer/grounding question
Sparky42 Offline
New Member

Registered: 06/22/16
Posts: 2
Loc: CA
Application is an outdoor 30kVA, 480V/400V step down delta-wye transformer to be located within 10 feet of a building panel breaker box. The box has three phase 480V fused power and an input ground wire tied to the breaker box via a screw lug. The output is a 3P4W IEC-309 receptacle, the ground pin of the receptacle has a wire that screws into the breaker box. My question is: Can I use the receptacle ground wire to be the ground for the transformer chassis and X0 of the secondary (via a terminal bar inside and bonded to the transformer enclosure)? Or will I have to run a ground wire independent of the receptacle so that ground is always made regardless of if the plug is in the receptacle. I could not find this detail in NEC.

Top
2014 / 2011 NEC & Related Books and Study Guides
#217354 - 06/23/16 12:20 AM Re: Outdoor transformer/grounding question [Re: Sparky42]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
I suppose you need to back up and see if that transformer is listed for cord and plug connection. If that is OK, I suppose the pin in the plug is sufficient to establish the ground.
Those 309 plugs are designed so the ground makes before the ungrounded pins.
_________________________
Greg Fretwell

Top
#217387 - 06/30/16 09:59 PM Re: Outdoor transformer/grounding question [Re: Sparky42]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Read 2014 N.E.C. 250.30 (C)

Top
#217393 - 07/04/16 09:09 PM Re: Outdoor transformer/grounding question [Re: Sparky42]
Sparky42 Offline
New Member

Registered: 06/22/16
Posts: 2
Loc: CA
Hmmm, the breaker box is mounted on a metal building. Can I consider the breaker box as the source location? In that case there is a ground wire connected to the breaker box itself (and it comes out via the IEC-309 connector). This is not a permanent installation it will only be active for a month or so.