The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 196 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#217341 - 06/21/16 07:31 PM grounding a ct cabinet
lite bulb Offline
Member

Registered: 02/12/06
Posts: 77
Loc: wilm,de.
I have a 800 amp service can I put just one 3/0 in one of the conduits from the main panel to ground the ct cabinet

Top
2014 / 2011 NEC & Related Books and Study Guides
#217342 - 06/21/16 07:59 PM Re: grounding a ct cabinet [Re: lite bulb]
ghost307 Offline
Member

Registered: 05/09/05
Posts: 884
Loc: Chicago Illinois USA
No.
A fully rated grounding conductor must be routed in each of the conduits for parallel conductors.
_________________________
Ghost307

Top
#217343 - 06/21/16 08:19 PM Re: grounding a ct cabinet [Re: lite bulb]
lite bulb Offline
Member

Registered: 02/12/06
Posts: 77
Loc: wilm,de.
thanks thats a 3/0 in each conduit right?


Edited by lite bulb (06/21/16 08:22 PM)

Top
#217344 - 06/22/16 04:34 AM Re: grounding a ct cabinet [Re: lite bulb]
ghost307 Offline
Member

Registered: 05/09/05
Posts: 884
Loc: Chicago Illinois USA
Copper or Aluminum?
_________________________
Ghost307

Top
#217347 - 06/22/16 07:18 AM Re: grounding a ct cabinet [Re: lite bulb]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Are you installing the GECs to the bond the neutrals in the CT? Or are you providing a bonding conductor for the CT cabinet?

Our POCO does not allow GECs in the CT cabinet, just bonding bushings IF required. Hot sequence the neutral block is bonded to the cabinet; cold sequence the neutral must 'float'. Then, bonding bushings may be required, dependent on the wiring method.

But, you are in Delaware, and Ghost is in Chicago, and I'm in NJ & referring to PSE&G rules.
_________________________
John

Top
#217348 - 06/22/16 07:56 AM Re: grounding a ct cabinet [Re: lite bulb]
ghost307 Offline
Member

Registered: 05/09/05
Posts: 884
Loc: Chicago Illinois USA
If you're installing 2 sets of 500kcmil as Service conductors, you'll need to use NEC table 250-66 to size the ground conductor in each conduit.
_________________________
Ghost307

Top
#217352 - 06/22/16 08:27 PM Re: grounding a ct cabinet [Re: lite bulb]
lite bulb Offline
Member

Registered: 02/12/06
Posts: 77
Loc: wilm,de.
Main service is comming into the ct cabinet in pvc, leaving the cabinet to a metal trough also pvc, out of the trough to the 800 amp main panel also pvc. I'll have to check on grounding the ct cabinet with the power company but I still need to ground the trough bonding will be done in main panel. Wire is 500 copper.


Edited by lite bulb (06/22/16 08:39 PM)

Top
#217355 - 06/23/16 06:57 PM Re: grounding a ct cabinet [Re: lite bulb]
lite bulb Offline
Member

Registered: 02/12/06
Posts: 77
Loc: wilm,de.
Power company does want a ground to the ct cabinet from main panel do I need a 3/0 in each conduit to the ct cabinet from the main panel or can I just put one 3/0 in one conduit also grounding the trough?


Edited by lite bulb (06/23/16 06:59 PM)

Top
#217358 - 06/24/16 01:51 PM Re: grounding a ct cabinet [Re: lite bulb]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
The POCO wants a "ground" in your CT cabinet; do they want the enclosure 'bonded' or the neutrals and GECs bonded at the CT enclosure?

IMHO, the POCO is looking to have the CT 'bonded'.
_________________________
John

Top
#217365 - 06/24/16 11:38 PM Re: grounding a ct cabinet [Re: lite bulb]
lite bulb Offline
Member

Registered: 02/12/06
Posts: 77
Loc: wilm,de.
The enclocure bonded