The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
breaker meltdown
by crselectric
09/24/16 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 15
sparky 9
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 264 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#216990 - 03/25/16 11:14 PM 3 phase star heater confusion
johno12345 Offline
Member

Registered: 09/13/05
Posts: 93
Loc: United Kingdom
Hello, its been a while!

I have a heat pump with a 6kW 3ph star electric accessory heater

I thought it wasn't working properly, and to cut a long story short, I clamped the terminals, and got a load reading on only one phase.

I have drawn it out, to try and make sense of it. I have a theory as to why its working as it is, but ill get to that in a later post.

_________________________
I took my time, I hurried up, The choice was mine, I didn't think enough

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#216991 - 03/26/16 03:58 AM Re: 3 phase star heater confusion [Re: johno12345]
geoff in UK Offline
Member

Registered: 12/30/02
Posts: 169
Loc: UK
The only way I can see those readings occurring is if heater 1 is open circuit but with an earth fault at the right hand end. Heater 3 must also be o/c or have no supply.

Top
#216992 - 03/26/16 09:27 AM Re: 3 phase star heater confusion [Re: johno12345]
ghost307 Offline
Member

Registered: 05/09/05
Posts: 876
Loc: Chicago Illinois USA
The only way that those amperage readings make any sense to me is if HEAT3 (or LS3) is open and HEAT1 is shorted to ground on the line side.
That would leave HEAT2 as the only working element; but it's using the metal housing as the return path instead of being routed to L1 via the HEAT1 coil.
_________________________
Ghost307

Top
#216993 - 03/26/16 09:38 AM Re: 3 phase star heater confusion [Re: johno12345]
johno12345 Offline
Member

Registered: 09/13/05
Posts: 93
Loc: United Kingdom
that's what I think is happening too. (its what I alluded to in the first post)

I don't think it would operate any cpd either. I didn't get a shock touching the case of the unit. It's still a safety issue though.

woulnt this happen if any element went down to ground though, and not operate the cpd? The only way to protect it would be to install a RCBO/RCD (GFI)
_________________________
I took my time, I hurried up, The choice was mine, I didn't think enough

Top
#216994 - 03/26/16 02:17 PM Re: 3 phase star heater confusion [Re: johno12345]
ghost307 Offline
Member

Registered: 05/09/05
Posts: 876
Loc: Chicago Illinois USA
The breaker won't trip until it sees more current than it's rated at. Depending on where the short is the current value on any given phase may not get high enough.

A GFI might do the trick; but only if the return current isn't somehow coming back on one of the phase legs.
If this was something expensive I'd suggest a protective relay that would operate if the current on the 3 legs differ from one another.
_________________________
Ghost307

Top
#216995 - 03/26/16 02:34 PM Re: 3 phase star heater confusion [Re: johno12345]
johno12345 Offline
Member

Registered: 09/13/05
Posts: 93
Loc: United Kingdom
its not something expensive, its just a heat pump with the accessory heater.

I can understand how it's all working as it is, it just sounds a bit alarming

it must be a fairly common failure mode for these things
_________________________
I took my time, I hurried up, The choice was mine, I didn't think enough

Top
#216996 - 03/26/16 06:35 PM Re: 3 phase star heater confusion [Re: johno12345]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
My guess is it started with the ground fault on heater 1, that one blew along with #3 because now they are seeing 120v instead of 104v and #2 is living on borrowed time.

What is the name plate power consumption? 3KW?

_________________________
Greg Fretwell

Top
#216997 - 03/26/16 07:24 PM Re: 3 phase star heater confusion [Re: johno12345]
johno12345 Offline
Member

Registered: 09/13/05
Posts: 93
Loc: United Kingdom
6.9kW, and its 400v between phases, so if the earth fault is where you have drawn it, heater 2 is seeing 230v, rather than 400
_________________________
I took my time, I hurried up, The choice was mine, I didn't think enough

Top
#216998 - 03/26/16 07:56 PM Re: 3 phase star heater confusion [Re: johno12345]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
The heaters are in series so the phase to phase voltage is split between them. Unfortunately I am still having the numbers to come out right with this calculator.
https://www.watlow.com/reference/tools/3phase.cfm


_________________________
Greg Fretwell

Top
#216999 - 03/27/16 09:25 AM Re: 3 phase star heater confusion [Re: gfretwell]
LarryC Offline
Member

Registered: 07/05/04
Posts: 775
Loc: Winchester, NH, US
Greg,

Since there is no contactor for the third phase, they may be using a corner grounded delta. In that case, the heating element will see the full 400 V across it and the current will be approximately double of the calculated. That comes a bit closer to the measured values.