#216947 - 03/18/16 11:51 AM 110.26(E)
triple Offline
Member
Registered: 04/01/02
Posts: 184
Loc: Wisconsin
Since most large switchboards placed along a wall tend to be positioned at least a few inches off/away from said wall, does the code allow foreign equipment to be mounted within this gap and under 6' above the electrical equipment? Tecnically, nothing placed within this gap would be within the "footprint" of the gear. Obviously, at some point, the gap does become large enough for other trades to use. Is it one inch, three inches, one foot? Can the AHJ say that even 18" isn't enough?
Top
2017 / 2014 NEC & Related Books and Study Guides
#216948 - 03/18/16 01:12 PM Re: 110.26(E) [Re: triple]
ghost307 Offline
Member
Registered: 05/09/05
Posts: 900
Loc: Chicago Illinois USA
Check with your AHJ.
I know that although Chicago says no (because they prohibit foreign items within the footprint and the associated working space); it is allowed in other cities.
_________________________
Ghost307
Top
#216954 - 03/18/16 10:37 PM Re: 110.26(E) [Re: triple]
triple Offline
Member
Registered: 04/01/02
Posts: 184
Loc: Wisconsin
The working space is only in front of the type of equipment I am referring to. For equipment requiring working space behind it, the unit would not be allowed to be placed up against a wall. Sorry, I don't think I described the situation very clearly.
Top
#216956 - 03/19/16 09:10 AM Re: 110.26(E) [Re: triple]
ghost307 Offline
Member
Registered: 05/09/05
Posts: 900
Loc: Chicago Illinois USA
I really think the AHJ needs to weigh in on this.
A drain line behind the equipment will cause few problems, a water line could sweat or break, a gas line is a hazard next to electrical equipment.
You also have to consider how you would repair/replace something that is rendered inaccessible after installation.
The 2 of you need to go over the specifics of this installation...I doubt that there is a universal answer to this.
_________________________
Ghost307
Top
#216957 - 03/19/16 10:53 AM Re: 110.26(E) [Re: triple]
triple Offline
Member
Registered: 04/01/02
Posts: 184
Loc: Wisconsin
1) The area I am referring to is above the equipment, within six feet vertically of its top, but behind the footprint. If the equipment were 6' from the wall instead of 4" then there would definately be no problem with anything foreign being installed there.
2) Nothing is rendered inaccessible. Again, I must not have described the scenario well. Nothing has been placed directly behind the switchgear. It it above but behind the footprint.
Top
#216970 - 03/21/16 06:34 AM Re: 110.26(E) [Re: triple]
ampherder Offline
Member
Registered: 09/29/11
Posts: 19
Loc: VA
The way 110.26(E) is worded, there would be nothing prohibiting what you describe. The AHJ can always choose to rule differently.
Top
#216976 - 03/22/16 06:57 AM Re: 110.26(E) [Re: triple]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
IMHO, it would depend on the proposed 'foreign' item is. Any 'item' that may 'leak' or cause any type of damage to the gear would be a "No", unless protection of the gear could be maintained.

The best solution to your inquiry would be a discussion with the local AHJ.
_________________________
John
Top
#216977 - 03/22/16 07:57 AM Re: 110.26(E) [Re: triple]
ghost307 Offline
Member
Registered: 05/09/05
Posts: 900
Loc: Chicago Illinois USA
Agreed.
I had a major switchgear installation where the Contractor took a short cut and routed the incoming natural gas line over the gear.
His response to the AHJ's objection was to put a drip pan underneath the gas pipe.

As the old adage goes...you can't fix stupid.
_________________________
Ghost307
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (Admin), 60 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals