#216940 - 03/16/16 08:40 AM Confusion with 250.90 (2011)
BigB Offline
Member
Registered: 03/31/04
Posts: 727
Loc: Tucson, AZ USA
250.92(B) says bonding jumpers....shall be used around impaired connections..... and in the same paragraph goes on to say that standard lock nuts or bushings shall not be the only means for the bonding required by this section. I thought the second sentence referred back to the first sentence where jumpers are required around impaired connections. An associate says no, the second sentence refers to all connections on the utility side of the service whether impaired or not.

Further confusion arises in 250.92(B)(3) where it allows threadless connectors made up wrench tight. What is the difference if a threadless connector is used with a standard lock nut versus a threaded piece of RMC using standard lock nuts?


Edited by BigB (03/16/16 08:41 AM)
Top
2017 / 2014 NEC & Related Books and Study Guides
#216944 - 03/18/16 07:41 AM Re: Confusion with 250.90 (2011) [Re: BigB]
HotLine1 Online   content


Member
Registered: 04/03/02
Posts: 6833
Loc: Brick, NJ USA
BigB:

Utility requirements may be 'above and beyond' NEC rules.
_________________________
John
Top
#216951 - 03/18/16 09:00 PM Re: Confusion with 250.90 (2011) [Re: HotLine1]
BigB Offline
Member
Registered: 03/31/04
Posts: 727
Loc: Tucson, AZ USA
Originally Posted By HotLine1
BigB:

Utility requirements may be 'above and beyond' NEC rules.


Not our POCO. The only thing they are concerned with is their ability to access the meter for non-payment lockout and that their side is locked and sealed.
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (Admin), 89 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/01/07
Posts: 62

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals