The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Live Chat Feature
by Ruben Rocha
Today at 03:39 PM
Safety at heights?
by gfretwell
Yesterday at 07:16 PM
failed home inspection.
by gfretwell
Yesterday at 07:03 PM
Webmaster > Admin
by Admin
Yesterday at 05:49 PM
Old Bath Fan
by gfretwell
Yesterday at 01:38 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Admin 33
HotLine1 20
Ruben Rocha 17
gfretwell 15
Trumpy 13
Who's Online
0 registered (), 0 Guests and 189 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#216614 - 01/04/16 09:35 PM supplemental grounding
watersparkfalls Offline
Member

Registered: 03/08/05
Posts: 210
Loc: Washington...Not DC
OK I feel like I should know this off the top of my head, but I am drawing a blank. First question is simply "Can the supplemental grounding electrode conductor go from panel to first ground rod and from that first ground rod to the second in two separate pieces of wire?" In other words use 4 acorns and 2 separate pieces of wire. And secondly when installing a 400 amp service with 2 qty 200 amp panels can I run from the ground rods to the first panel and then unbroken to the second panel/ Or does each service require its own supplemental grounding conductor?

Thanks,
H20

Top
2017 / 2014 NEC & Related Books and Study Guides
#216615 - 01/04/16 09:38 PM Re: supplemental grounding [Re: watersparkfalls]
gfretwell Offline


Member

Registered: 07/20/04
Posts: 9065
Loc: Estero,Fl,usa
Yes, you can splice to a supplemental electrode

From the handbook



BTW does anyone see the anomaly in the code, demonstrated in the exhibit.
_________________________
Greg Fretwell

Top
#216625 - 01/06/16 08:29 PM Re: supplemental grounding [Re: watersparkfalls]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Yes, you can splice to a supplemental electrode

Ist you MUST make sure it is a supplemental Grounding Conductor not required by Code.

See 250.52./250.53/ 250.64

Splicing 250.64 C

Taping 250.64 D