The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 227 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#216438 - 12/18/15 05:30 AM Nail salon ventilation
sparkync Offline
Member

Registered: 10/17/02
Posts: 811
Loc: NC
I'm checking a job(nail salon) that requires ventilation. The safety inspector left a paper with the owner that says that "systems shall be capable of exhausting a minimum of
50 cfms per station. Has anyone run across one of these? The business I am looking at has around 6 chairs for customers. I'm guessing that if I put a 300 cfm fan in the middle that should do it. I left a message with one of the inspectors, but they have not returned my call. Any ideas?
Thanks

Top
2014 / 2011 NEC & Related Books and Study Guides
#216443 - 12/18/15 11:35 AM Re: Nail salon ventilation [Re: sparkync]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
I'd ask the inspector! Better yet, find the exact code he's using, and see what the code says.

Evacuation of solvent fumes is a BIG inspection issue for nail salons. Be sure to take into account the cfm lost in every bend of the pipe. Be sure to provide for make-up air.

As I recall it, the ventilation needs to be present at each station; general room ventilation won't satisfy the requirement. They might let you put the fans on timers. I quoted one such job, only to have the owner choose to play inspection / responsibility games instead. Oh well. frown

Top
#216472 - 12/20/15 10:35 AM Re: Nail salon ventilation [Re: sparkync]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
sparkync:

A ventilation system for nail salons here is required to have a plan prepared by an Architect or Engineer.

Usual is a 'common' exh fan, trunk duct. and a 'drop' at each workstation. Some have a 'on/off' switch at each station, some are a 'one switch' control at reception.

IMHO, the mechanical install of this type of system is best left to a mechanical contractor (HVAC).
_________________________
John

Top
#216480 - 12/20/15 10:14 PM Re: Nail salon ventilation [Re: sparkync]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
I agree with John. Just ask the HVAC guy where he needs the power and be done with it. Around here, he needs to run the duct anyway if it is more than a short 4" flex to the nearest "out". (no venting in the attic or anything)
_________________________
Greg Fretwell

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals