The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
breaker meltdown
by crselectric
09/24/16 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm≤ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 9
sparky66wv 8
gfretwell 8
Vlado 6
Who's Online
1 registered (Texas_Ranger), 273 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#216435 - 12/16/15 03:42 PM Internet bonding to sub-panel
flitch Offline
New Member

Registered: 12/15/15
Posts: 2
Loc: Western NY
Homeowner has Time Warner internet telephone cable direct to sub-building. Sub-building serviced by 4 wire 150A sub-panel fed from main 200A panel 100 feet away with ground rods located (1) at the main panel and (2) at the sub-panel, both bonded back to their respective ground bus. The sub-building has gas heat so the CSST pipe is bonded to the ground rod (for convenience) vs being bonded inside the panel. Can the internet cable be bonded to the same rod which would then make a loop of the internet cable directly from the sub-panel (via the cable) to the pole? Isnít this likely to be current surge problem for the internet cable fed devices.

Top
2014 / 2011 NEC & Related Books and Study Guides
#216436 - 12/16/15 05:45 PM Re: Internet bonding to sub-panel [Re: flitch]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
More grounding is better in a surge situation. You want a single point ground on your side of the building entrance, preferably right where the main bonding jumper connects to the grounding electrode conductor (same bus bar). That should be where the inter system grounding bus lands. Any "loop" created on the line side is your phone company's problem and they are well prepared to deal with it. They reground their stuff at every drop.
_________________________
Greg Fretwell

Top
#216442 - 12/18/15 11:31 AM Re: Internet bonding to sub-panel [Re: flitch]
flitch Offline
New Member

Registered: 12/15/15
Posts: 2
Loc: Western NY
Thanks, Greg.