#21609 - 02/06/03 08:06 AM Sizing Emergency Generator
Frank Cinker Offline
Member
Registered: 07/29/01
Posts: 311
Loc: Pennsylvania
I was called upon to size an emergency generator as an alternate power source for a fire pump. There are other loads as well. However, I want to focus on the fire pump load for now. I plan to use the horsepower rating of the motor to calculate load. I reviewed the 2002 NEC Handbook 695.3(B)(1)and learned the generator does not need to be sized for lock rotor of fire pump.
<b>Where the alternative source of power is an on-site generator, the alternative source disconnecting means and the alternative source overcurrent protective device(s) for the electric-drive fire pump are not required to be sized for locked-rotor current of the fire pump motor(s). Rather, the circuit components of the alternative source are permitted to be sized according to Article 430, provided they are “selected or set to allow instantaneous pickup and running of the fire pump load.” See 445.12(A). <b/>
Did I interpret it properly?
Top
Work Gear for Electricians and the Trades
#21610 - 02/06/03 02:52 PM Re: Sizing Emergency Generator
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
If your fire pump has it's rotor locked indefinitely, it's a much bigger problem.(that should have been corrected earlier)
I believe you're correct...S
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 67 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals