#216079 - 09/24/15 10:19 PM bonding bushing
watersparkfalls Offline
Member
Registered: 03/08/05
Posts: 212
Loc: Washington...Not DC
what is the code article that specifically states where and when bonding bushing is required for transformers?
I am installing a transformer with concentric knockouts that
I won't knock all out, usually I knock out my own eccentric and don't need one.

I beleive it is only required on the load side?

What if I bond XO at panel where I punch my own, would I still need one in x-former?

Thanks,
H20
Top
2017 / 2014 NEC & Related Books and Study Guides
#216080 - 09/26/15 06:25 PM Re: bonding bushing [Re: watersparkfalls]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
I think the general rule you use bonding bushings on raceways containing unfused conductors like services. I suppose if you have a transformer secondary conductor before it gets to the first O/C device it should have bonding bushings but I am not sure that is code.
_________________________
Greg Fretwell
Top
#216091 - 09/30/15 05:56 PM Re: bonding bushing [Re: watersparkfalls]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
I think Soares is the source of this.

I think in terms of the bonding bushings being used on the 'service' side of any separately derived source, over that portion where the 'ground' is lacking and before the neutral bond.
Top
#216140 - 10/12/15 06:05 PM Re: bonding bushing [Re: watersparkfalls]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
Don't forget 250.97 2014 N.E.C. . Bonding over 250 volts to ground .
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 61 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals