The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
1 registered (gfretwell), 194 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#216059 - 09/20/15 03:18 PM feeder calculations
watersparkfalls Offline
Member

Registered: 03/08/05
Posts: 210
Loc: Washington...Not DC
trying to figure out this 110.14(c) and why it lets you use the 90 degree column for derating when more than 3 current carrying conductors applies... is this for everything feeders, branch circuits? I always thought if you land in a lug (disco, panel) you had to calculate using the 75 degree column.
thanks,
H2o

Top
2014 / 2011 NEC & Related Books and Study Guides
#216061 - 09/20/15 05:57 PM Re: feeder calculations [Re: watersparkfalls]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
H2O:

Basically, in a short, plain English statement; you can use the 90 degree col. for derating calculations, but you must not exceed the 60 or 75 degree maximums after your calculations.
_________________________
John

Top
#216062 - 09/20/15 06:04 PM Re: feeder calculations [Re: watersparkfalls]
gfretwell Online   content

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
The 75c is for the lug. With a simple 3 wires in a pipe, that will usually be the limiting factor.
As soon as you get more wire in the pipe and start running it through hostile areas where you have "adders" on, you are happy you can start from 90 and the wire is still going to be the limiting factor.
_________________________
Greg Fretwell

Top
#216068 - 09/21/15 07:40 AM Re: feeder calculations [Re: watersparkfalls]
ghost307 Offline
Member

Registered: 05/09/05
Posts: 884
Loc: Chicago Illinois USA
Also; you can only start in the 90 degree column if the insulation is rated at 90 degrees...like THHN is.
_________________________
Ghost307

Top
#216069 - 09/21/15 09:42 AM Re: feeder calculations [Re: watersparkfalls]
gfretwell Online   content

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
90c is becoming the norm these days since the introduction of THWN-2 and the dual rated THHN/THWN-2 conductor.
You still need to be sure what you have but what you need is usually available.
_________________________
Greg Fretwell

Top
#216072 - 09/21/15 10:53 PM Re: feeder calculations [Re: watersparkfalls]
Scott35 Offline

Broom Pusher and
Member

Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
To elaborate:

If the Insulation is rated for 90C, the derating may begin at the Ampacity in that column, per Table 310.16; however the actual Termination Ampacity is based on the 60C Column (for Conductors size #2 and smaller), or the 75C Column (for Conductors size #1 and larger).

Examples:

Ex. 1:
(2) 20 Amp 3 Phase 4 Wire multiwire Circuits run in single Raceway.

All Conductors are #12 THHN CU., and are Current Carrying; total of (8) Current Carrying Conductors.

Derating value for 7-9 Conductors = 0.7
Table 310.16 Ampacity for #12 THHN CU. at 90C = 30 Amps.
30 Amps X 0.7 = 21 Amps
Maximum OCPD is 20 Amps (for general circuits)

The derated value of 21 Amps is greater than the Maximum OCPD rating of 20 Amps, therefore the Circuits Terminated to 20 Amp OCPD's are compliant.

............................................................

Ex. 2:
(3) 30 Amp 3 Phase 4 Wire multiwire Circuits run in single Raceway.

All Conductors are #10 THHN CU., and are Current Carrying; total of (12) Current Carrying Conductors.

Derating value for 10 - 20 Conductors = 0.5
Table 310.16 Ampacity for #10 THHN CU. at 90C = 40 Amps.
40 Amps X 0.5 = 20 Amps
Maximum OCPD for #10 CU is 30 Amps (for general circuits).
Derated value of 20 Amps is less than the maximum OCPD value of 30 Amps; therefore, to be compliant, the Circuits will be Terminated to 20 Amp OCPD's.

That is a basic version of the derating methods.

Feel free to respond.

--Scott (EE)