The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
breaker meltdown
by sparky
Yesterday at 07:30 PM
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 13
sparky 10
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 258 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#216019 - 09/07/15 05:47 PM 2500 amp service
Merlin Offline
Member

Registered: 01/27/04
Posts: 170
Loc: NW Indiana
Looking for some suggestions.....I am quoting a job to install a 2500 amp, 480/277V service. This will be feed from a pad mount transformer about 30 feet into a building. Obviously it will be parallel conductor fed. What combination would you all use? 750kcmil, 1000kcmil,.....any thoughts?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#216020 - 09/07/15 05:56 PM Re: 2500 amp service [Re: Merlin]
twh Offline
Member

Registered: 03/11/04
Posts: 892
Loc: Regina, Sask.
Aluminum. Then, all sizes are easy.

Top
#216021 - 09/07/15 06:35 PM Re: 2500 amp service [Re: Merlin]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
Merlin:

Common is 6 sets of 600 KCMil Cu THHN/THWN in 4" PVC

You have to check the secondary 'window' of the pad mount xfr., as that limits the quantity of conduits you can install.
_________________________
John

Top
#216042 - 09/15/15 09:19 PM Re: 2500 amp service [Re: HotLine1]
Merlin Offline
Member

Registered: 01/27/04
Posts: 170
Loc: NW Indiana
Correct me if I'm wrong, but 6-600's would be
6 x 475 = 2850.
Derated for 4 conductors in conduit(480/277) at 80%
2850 x .8 = 2280.

Wouldn't it be 6x750kcmil?
6 x 535 = 3210
3210 x .8 = 2568

Top
#216045 - 09/16/15 08:35 AM Re: 2500 amp service [Re: Merlin]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
Merlin:
I stand corrected....I did not 'see' 2500 amps.
_________________________
John

Top
#216073 - 09/21/15 11:10 PM Re: 2500 amp service [Re: Merlin]
Scott35 Offline

Broom Pusher and
Member

Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
If this Installation is for Service Feeders (from a Poco Transformer to Service Equipment), you need to verify the requirements with the Service Planner before bidding this Project (or before commencing the actual work!)

If the Installation is on the LOAD side of the Service Disconnect, then (6) 4" Ducts with 4-750MCM CU. per duct is sufficient... if NO Equipment Grounding Conductors are installed!

If an EGC is to be installed, that will be a minimum of (1) 350MCM CU. per duct, so now the Ducts would be 5" (???)
dunno

--Scott (EE)
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Top