The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 8
Trumpy 6
Who's Online
0 registered (), 261 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#215727 - 07/07/15 05:50 PM VFD working space?
triple Offline
Member

Registered: 04/01/02
Posts: 182
Loc: Wisconsin
Does 110.26(A) apply to variable frequency drives controlling hvac related pumps? The wording of the article (and the commentary in the NEC Handbook) definitely seems to suggest that vfd's require working space. However, the electrical inspector is allowing them to be buried behind the motors and pumps. "Examining, adjusting, serving, and maintaining" these "controls" for "heating and air-conditioning equipment" now requires standing over/on or straddling the motor/pump unit.

Top
2014 / 2011 NEC & Related Books and Study Guides
#215728 - 07/07/15 05:52 PM Re: VFD working space? [Re: triple]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
triple:
Based on what you say, IMHO I would say 'red tag'.
_________________________
John

Top
#215734 - 07/09/15 08:48 AM Re: VFD working space? [Re: triple]
ghost307 Offline
Member

Registered: 05/09/05
Posts: 884
Loc: Chicago Illinois USA
I agree...red tag.
_________________________
Ghost307

Top
#215834 - 07/25/15 06:50 AM Re: VFD working space? [Re: triple]
tsolanto Offline
Member

Registered: 09/03/02
Posts: 131
Loc: Long Island NY
I looked through 430 to see if there were any exceptions for Adjustable Speed Drives. I could not find any. So, IMO 110.26 applies.

"430.120 General. The installation provisions of Part I
through Part IX are applicable unless modified or supplemented
by Part X."


I could not find anything in Part 1 through 10 to suggest anything with regards to working space. I would have hoped that it pointed you to 110.26 at some point but it does not.

Some people consider a VFD a motor control center and if you look at it that way you would need to comply with 110.26F. I don't believe that it is a MCC since there is a clear section in 430.120 specifically providing rules for Adjustable Speed Drives (VFD's)...

IMO 110.26 A as you suggest is the winner.


Edited by tsolanto (07/25/15 06:52 AM)

Top
#215835 - 07/25/15 06:51 AM Re: VFD working space? [Re: triple]
tsolanto Offline
Member

Registered: 09/03/02
Posts: 131
Loc: Long Island NY
All that being said, here in NYC believe it or not we are still on the 2008 NEC so my commentary is based on that. I don't know which edition you are working with, not sure if it would matter in this case either.

Top
#215836 - 07/25/15 11:00 AM Re: VFD working space? [Re: triple]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
IMHO, there are no differences within '11 or '14 regarding this.

NJ is still on'11, and I don't recall anything from '14 from "the changes" although I still admit to have a lot of reading....
_________________________
John

Top