#2157 - 06/23/01 06:05 PM Surge?
CandCTech Offline
Junior Member
Registered: 06/23/01
Posts: 3
Loc: Clinton, Ma. USA
Just wondering if anyone has any suggestions? Here is the problem; all the lights in the house dim when the condensor of the centeral air comes on. The centeral air unit is on a 20A DP breaker, so it's not just one phase affected.
Thanks in advance.
Top
Work Gear for Electricians and the Trades
#2158 - 06/23/01 06:30 PM Re: Surge?
Anonymous
Unregistered

It could be normal. It could be that the service doesn't have enough KVA available to avoid a noticeable drop when the motor starts.

How old is the motor? Are there leaves in the fan? Has this been a problem since it was installed?

How many houses run off your transformer?
Top
#2159 - 06/23/01 07:05 PM Re: Surge?
Redsy Offline
Member
Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Go back to the topic titled "Whats the problem?" on 6-2-01. This was discussed in depth. Most of the replies will apply to your question here.
Top
#2160 - 06/23/01 07:24 PM Re: Surge?
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 4196
Loc: NY, USA
It would be a good Idea to first rule out loose connections. Check all of them.

Bill
Top
#2161 - 06/23/01 08:10 PM Re: Surge?
CandCTech Offline
Junior Member
Registered: 06/23/01
Posts: 3
Loc: Clinton, Ma. USA
I'll check out that "What's the problem". It's brand new, connections are fine, no obstructions of any kind. I was thinking it was a power company problem myself but I was wondering if I was overlooking another possible problem. If it is the power company I'm not aware of any solutions, it's tough getting them to do anything. I was wondering if there is anything on the market to make up for a problem like this for a reasonable amount of money? I know a VFD or soft-start would solve the problem but that seem's a little extreme.
Thanks for the responses, I appreciate it. I stumbled on to this site today, I now have it bookmarked it's a great site.
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (Ruben Rocha), 155 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals