The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
1 registered (sparkyinak), 220 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#21563 - 02/05/03 10:02 AM Mercury Vapor light problem
rayh78 Offline
Member

Registered: 11/11/01
Posts: 26
Installed a 100 watt mercury vapor outdoor light. It was fine until winter now its going thru bulbs. Problem started when customer is using a small electric space 1500watt heater on inside on same circut.
Is it a defective fixture or to much on circut.
Thanks

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#21564 - 02/06/03 03:27 PM Re: Mercury Vapor light problem
golf junkie Offline
Member

Registered: 04/22/01
Posts: 511
Loc: York, NE
What voltage do you have at the light with both the heater and light drawing current??

GJ

Top
#21565 - 02/06/03 06:50 PM Re: Mercury Vapor light problem
rayh78 Offline
Member

Registered: 11/11/01
Posts: 26
did not check, assumed if it was drawing to much would trip breaker

Top
#21566 - 02/06/03 08:00 PM Re: Mercury Vapor light problem
nesparky Offline
Member

Registered: 06/21/01
Posts: 650
Loc: omaha,ne
The 100 watt light draws about.9 amp (100W/110V=.9091A)
The 1500 watt space heater draws (1500w/110v=13.6364A)
total draw is 14.5455A
A 20 Amp breaker will carry this all day.
A 15 amp breaker will propally carry this if the heater does not run all the time.
If 14AWG wire was used and the heater and light are over50-75' away you propably have a voltage drop causing the light to pull more than normal. If so the bulb will heat up more than normal and burn out much to soon.
You need to do a voltage check at the circuit breaker feeding this circuit and at the heater and at the light. Be careful and use a good quality meter. Avoltage drop of greater than 5% is a problem.
You may need to seperate the heater and light. Also check if anything else is on the circuit.
Good luck
_________________________
ed

Top
#21567 - 02/07/03 05:50 PM Re: Mercury Vapor light problem
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Ray,
One thing I do know, is that any type of Gas
Discharge lighting, does not particularly like Voltage drop, it can damage the control gear as well as the lamps.
If possible, I would put the MV Lighting on a dedicated circuit.
Hope this helps.