The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
breaker meltdown
by crselectric
09/24/16 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 18
sparky 9
gfretwell 9
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 253 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#215603 - 06/07/15 10:55 PM Unfused surge protection
twh Offline
Member

Registered: 03/11/04
Posts: 892
Loc: Regina, Sask.
Is it normal to install surge protection without a breaker? The surge protection in question has fuses and is on an 800 amp cdp. How would you change fuses without shutting down everything on the cdp, like the servers, office computers on three floors, the lights and the elevator?


Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#215604 - 06/07/15 11:58 PM Re: Unfused surge protection [Re: twh]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
I agree this may be a poor design but if there are fuses in the SP, it is legal. I suppose with the right PPE and tools you could change the fuses hot but the only reason they would fail is a fault in most cases (shorted MOV) and the new fuse is going to "flashbulb" most of the time.
I would put it on a breaker.
_________________________
Greg Fretwell

Top
#215612 - 06/09/15 04:52 PM Re: Unfused surge protection [Re: twh]
wa2ise Offline
Member

Registered: 11/29/02
Posts: 769
Loc: Oradell NJ USA
If this box claims to clamp transients of a few nanoseconds, the coil usually in circuit breakers may interfere with that. The coils would look like a high impedance to transient spikes that short. However, most power supplies in servers and computers contain filtering coils of much higher inductance, so such short transients shouldn't be much of an issue.

For longer transients, the circuit breaker shouldn't be an issue.

Top
#215613 - 06/10/15 06:38 AM Re: Unfused surge protection [Re: twh]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
As this is in Canada, IF the install is compliant with the CEC, it also conforms to the mfg. install guidelines.

"2.1.4 Wiring
Turn OFF the power to the electrical distribution
equipment where the CPS Filter is to be installed.
Install a branch circuit breaker to feed the CPS filter
device for ease of installation. The unit contains UL
and CSA approved fusing to protect against short
circuit fault conditions within the device.
Over current protection is not specifically required,
although most customers choose to install a circuit
breaker as a disconnect device on panelboards or
switchgear assemblies. (See Table 2 for suggested
circuit breaker size). Follow NEC, CEC and applicable
local codes when connecting the CPS directly to the
Bus Bar."

IMHO, a branch circuit CB as suggested within the guidelines would be the way to go, and how all I have seen are installed.
_________________________
John

Top