The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 109 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#215440 - 05/09/15 02:29 PM Sub panel
sparkync Offline
Member

Registered: 10/17/02
Posts: 811
Loc: NC
I have a 200 amp Meter/combo with feed through lugs, outside with 5 double pole breakers. I am feeding out of back of that panel to a 200 amp main breaker panel directly behind it. The panel inside now becomes a sub panel, therefore I will have to run an insulated neutral from the outside panel to the inside (4 wire), but can still come off the "feed through" lugs to the inside main breaker, right??
I guess I can actually have a main lug panel inside instead of a Main breaker since I'm using the Main breaker outside thru the feed through lugs. Thanks

Top
2014 / 2011 NEC & Related Books and Study Guides
#215446 - 05/10/15 12:42 PM Re: Sub panel [Re: sparkync]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Yes it could be an MLO but the inside disconnect is not a bad idea, if for nothing else to avoid confusion from a "home inspector" down the road. The 4 wire feeder and the isolated ground bus is right.
_________________________
Greg Fretwell

Top
#215453 - 05/11/15 01:06 PM Re: Sub panel [Re: sparkync]
sparkync Offline
Member

Registered: 10/17/02
Posts: 811
Loc: NC
Thanks Greg. Yes I'll probably go with the main breaker. I agree. Cuts down on confusion.