The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by gfretwell
01/17/17 01:16 PM
Why cables look like they do
by Texas_Ranger
01/17/17 12:33 PM
Re: Fabricating Guards out of Lexan?
by ghost307
01/17/17 11:21 AM
Would ELV branch circuits be a good idea?
by ghost307
01/17/17 11:18 AM
100% breakers?
by Texas_Ranger
01/16/17 06:13 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 19
Webmaster 14
Trumpy 12
ghost307 12
gfretwell 10
Who's Online
2 registered (ghost307, gfretwell), 0 Guests and 78 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#215440 - 05/09/15 02:29 PM Sub panel
sparkync Offline
Member

Registered: 10/17/02
Posts: 811
Loc: NC
I have a 200 amp Meter/combo with feed through lugs, outside with 5 double pole breakers. I am feeding out of back of that panel to a 200 amp main breaker panel directly behind it. The panel inside now becomes a sub panel, therefore I will have to run an insulated neutral from the outside panel to the inside (4 wire), but can still come off the "feed through" lugs to the inside main breaker, right??
I guess I can actually have a main lug panel inside instead of a Main breaker since I'm using the Main breaker outside thru the feed through lugs. Thanks

Top
2017 / 2014 NEC & Related Books and Study Guides
#215446 - 05/10/15 12:42 PM Re: Sub panel [Re: sparkync]
gfretwell Online   content


Member

Registered: 07/20/04
Posts: 9059
Loc: Estero,Fl,usa
Yes it could be an MLO but the inside disconnect is not a bad idea, if for nothing else to avoid confusion from a "home inspector" down the road. The 4 wire feeder and the isolated ground bus is right.
_________________________
Greg Fretwell

Top
#215453 - 05/11/15 01:06 PM Re: Sub panel [Re: sparkync]
sparkync Offline
Member

Registered: 10/17/02
Posts: 811
Loc: NC
Thanks Greg. Yes I'll probably go with the main breaker. I agree. Cuts down on confusion.

Top