#215362 - 04/15/15 09:34 PM Laundry Circuits
BigB Offline
Member
Registered: 03/31/04
Posts: 719
Loc: Tucson, AZ USA
If I provide an another circuit in the laundry in addition to the required 210.11(C)(2)branch circuit can this additional circuit have other outlets, like say an outdoor receptacle or two?
Top
2017 / 2014 NEC & Related Books and Study Guides
#215363 - 04/15/15 11:45 PM Re: Laundry Circuits [Re: BigB]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Yes, They only require one dedicated circuit 20a for the "laundry" but there can be other general lighting circuits in the room.
_________________________
Greg Fretwell
Top
#215364 - 04/16/15 08:27 AM Re: Laundry Circuits [Re: BigB]
BigB Offline
Member
Registered: 03/31/04
Posts: 719
Loc: Tucson, AZ USA
Thanks Greg. Specifically this extra circuit will be for two counter top receptacles in the laundry and one outdoor receptacle, all 20 amp GFCI protected. What got me thinking about it is the argument about the kitchen SABC circuits, no matter how many you provide after the required two they still cannot have other outlets except dining, nook, pantry etc. as I understand it, and as my jurisdiction enforces it.


Edited by BigB (04/16/15 08:28 AM)
Top
#215365 - 04/16/15 10:17 AM Re: Laundry Circuits [Re: BigB]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I think difference is that 210.11(C)(2) says "this circuit" when describing the laundry circuit. 210.52(B)(2) says "The two or more small-appliance branch circuits" implying all of them.
I suppose you need to ask your AHJ for the answer that applies in his patch.

At a certain point this dedicated circuit thing does go just a little nuts.
_________________________
Greg Fretwell
Top
#215366 - 04/16/15 12:29 PM Re: Laundry Circuits [Re: BigB]
HotLine1 Online   content


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
I agree with Greg.
Talk to your local AHJ for his take
_________________________
John
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 87 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals