#215315 - 04/07/15 08:21 PM Above ground pool
sparkync Offline
Member
Registered: 10/17/02
Posts: 809
Loc: NC
Been a while again since I've wired an above ground pool. Just wanting some refresher ideas.

The pool will be 52" high which will qualify it as a "permanent pool". Pump motor is 1 1/2 hp. on 120 volts.

If I run a 30 amp 4 wire 240 volt line in pvc conduit minimum of 18" deep, out to a 4x4 post and keep it at least 6ft. from the pool, set a small 4 or 6 circuit weatherproof panel, then come out the bottom of the panel and set a weatherproof bell box and put a 20 amp. 120 volt twist lock recpt. protected by a 20 amp GFCI breaker in the box ( with an in use cover of course) (or wire it direct), then come back out of the panel and put a regular GFCI outlet with an in use cover for the convenience outlet requirement, then dig a small trench around the pool and install #8 solid grd. wire and bond it at least 4 times to the frame of the pool then back to the pump, will this work? There's something about bonding the water I don't completely understand if you can comment on.

Hope this makes sense.

Thanks for the input.
Top
2017 / 2014 NEC & Related Books and Study Guides
#215316 - 04/07/15 10:44 PM Re: Above ground pool [Re: sparkync]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
If the ladder is metal, you bond the water when you bond the ladder. They do make a plumbing fitting for the purpose if you have no metal parts in the water.
The rest sounds reasonable.
_________________________
Greg Fretwell
Top
#215317 - 04/08/15 05:40 AM Re: Above ground pool [Re: sparkync]
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
Here is a gadget for grounding water...

http://www.munroelectric.com/silvereclip...fe.680.Pool.Kit

shortcircuit

Top
#215319 - 04/08/15 07:54 AM Re: Above ground pool [Re: sparkync]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Following all the above would result in a compliant install.

You may find that the skimmer unit supplied with the pool has a plate and lug to provide the water bond. IMHO, the AG pool mfgs should have to provide a point to connect the water bond, as it is required by the NEC.

_________________________
John
Top
#215821 - 07/22/15 08:40 AM Re: Above ground pool [Re: sparkync]
tsolanto Offline
Member
Registered: 09/03/02
Posts: 131
Loc: Long Island NY
Looks compliant to me
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 37 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals