#21516 - 02/04/03 07:49 PM Smoke Detectors
Anonymous
Unregistered

I was told that smokies had to be positioned inside a bedroom (centered off the door) 12 inches back, from one electrician. Then another electrician told me that it doesn't matter where you position it, yet it needs to be in the room. What the heck is the truth. Is it code related? Also, what should the height of a receptacle be, if you are boxing a single unit home?
Top
Work Gear for Electricians and the Trades
#21517 - 02/04/03 08:13 PM Re: Smoke Detectors
lighthouse Offline
Member
Registered: 01/02/03
Posts: 134
Loc: philadelphia pa 19125
The NFPA recommends smoke alarms be installed in EVERY room and area of your home or bulding for complete protection. For maximum protection, install at least one ionization and one photoelectronic smoke alarm on each level of your home.

All smoke alarms should be replaced after 10 years of operation. Ten years is a smoke alarm's useful lifetime and for continued, reliable safety and protection, smoke alarms need to be replaced.

Consumer's should consult their owner's manual for specific instructions when locating a smoke alarm. The following are some general guidelines:

Because smoke rises, smoke alarms should be installed on the ceiling or on walls at least 4 to 6 inches below the ceiling.

Smoke alarms should not be located less than 4 to 6 inches from where the wall and ceiling meet on either surface; this space is dead air that receives little circulation.

Smoke alarms should not be mounted in front of an air supply, return duct, near ceiling fans, peaks of A-frame ceilings, dusty areas, locations outside the 40 degree Farenheit to 100 degree Farenheit temperature range, in humid areas or near fluorescent lighting.
Top
#21518 - 02/04/03 08:16 PM Re: Smoke Detectors
nesparky Offline
Member
Registered: 06/21/01
Posts: 642
Loc: omaha,ne
The positioning of smoke detectors is in NFPA 72 Fire Alarm Code. They need to be away from wall and ceiling corners. ALmost all smokes have installation instructions for spacing and distances. The reason is that a smoke detector in the wrong place will not see the smoke thus delaying any alarm. It's a life safety issue.
A common receptacle height is 18" to center of box. For ADA heights check with your AHJ.
_________________________
ed
Top
#21519 - 02/04/03 09:16 PM Re: Smoke Detectors
bobp Offline
Member
Registered: 10/14/02
Posts: 70
Loc: Puyallup, WA, USA
You need to check with the AHJ. Many have amended the codes or written their own for placement and requirement of smoke detectors. I have two towns around here that require the bedroom smokes to be inside the door (no more than 18"), but the county and other towns just require them in the bedrooms. And please don't make me try and explain where each one wants the hall smokes.
Bob
Top
#21520 - 02/04/03 10:54 PM Re: Smoke Detectors
Electric Eagle Offline
Member
Registered: 04/20/02
Posts: 914
Loc: Alpharetta, GA
Our inspectors only want a smokey within 10 feet of every bedroom and one inspector recently told me not to put them inside the bedroom because of the new arc fault rule requiring all bedroom wiring to be arc fault protected and he didn't want the smokes on an arc fault circuit.
Top
#21521 - 02/05/03 08:50 AM Re: Smoke Detectors
pwood Offline
Member
Registered: 02/04/03
Posts: 67
Loc: castella,calif usa
the building codes say to install per manufacturer's instructions and per the code. further states that one to be installed in each sleeping room and centrally located in the corridor or area giving access to the sleeping rooms.AHJ'S may require installation per local preferences so it's wise to ask before installation if possible.
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 40 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals