#215142 - 03/08/15 03:19 PM steel bushings
triple Offline
Member
Registered: 04/01/02
Posts: 184
Loc: Wisconsin
Are steel bushings allowed on rigid pipe terminations for conductors #4 or larger? 300.4(G) appears to say no. When used on smaller conductors, is the steel bushing listed for use without a locknut inside the box?
Top
2017 / 2014 NEC & Related Books and Study Guides
#215143 - 03/08/15 03:41 PM Re: steel bushings [Re: triple]
triple Offline
Member
Registered: 04/01/02
Posts: 184
Loc: Wisconsin
Also, even though it is not stated in 352.46, I would assume steel bushing would not be allowed on PVC due to a lack of connection to ground. And to be clear, I am refurring to standard/non bond bushings in these post. The Handbook shows bond bushings being used without locknuts so it is probably safe to assume that doesn't violate their UL Listing.
Top
#215144 - 03/08/15 04:53 PM Re: steel bushings [Re: triple]
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Sure they're allowed ..... as long as they have an insulated throat.

Top
#215149 - 03/10/15 05:46 PM Re: steel bushings [Re: triple]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Where is it written that they must have plastic throats?

The current Steel City catalog shoes several styles of metal bushings. Some are zinc and some are iron. Several do not have any sort of liner. All show a current UL listing.

Or ... are these another 'forbidden fitting" to add to the other thread?
Top
#215152 - 03/11/15 06:19 AM Re: steel bushings [Re: triple]
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
300.4(G)
Insulated Fittings. Where raceways contain 4 AWG or larger insulated circuit conductors, and these conductors
enter a cabinet, a box, an enclosure, or a raceway, the conductors shall be protected by an identified fitting providing a smoothly rounded insulating surface, unless the conductors are separated from the fitting or raceway by identified insulating material that is securely fastened in place.


They could be listed if they're not intended to put conductors #4 or larger in the conduit.
Top
#215159 - 03/11/15 05:36 PM Re: steel bushings [Re: triple]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Well, that's enough to keep them from my 'illegal fittings' thread!

To be fair, I've only seen the metal bushings on 3/4 and 1/2 pipe. Not much room for big wires there! Plus, they've all been older jobs, quite possibly from the days before plastic.
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 37 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals