#214775 - 01/23/15 05:22 AM Understanding NEMA 5-15 / 5-20 Outlets
andey Offline
Member
Registered: 08/05/08
Posts: 35
Loc: germany
Hello guys,

I need a quick help in understanding from you as I'm in the process of assembling a machine for use in the US.

NEMA 5-15 Outlet with 15Amp breaker - OK.
NEMA 5-20 Outlet with 20Amp breaker accepts both 15Amp and 20Amp plugs.
If now a 5-15 extension cord with multiple outlets is inserted into the 5-20 Outlet, can't the cord be overloaded? Because the breaker rating is too high?

Thanks,
Andy
Top
Work Gear for Electricians and the Trades
#214777 - 01/23/15 07:05 AM Re: Understanding NEMA 5-15 / 5-20 Outlets [Re: andey]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6833
Loc: Brick, NJ USA
In theory (and the real world), yes the cord could be overloaded, based on the rating of the cord.

Does this happen? Yes.

Any issues?? Warm/hot cord; deterioration of the cord over time.

The NEC does not address what gets plugged into the 5-15 or 5-20, or any other devices, and for all intensive purposes we stop at the device.

_________________________
John
Top
#214778 - 01/23/15 08:39 AM Re: Understanding NEMA 5-15 / 5-20 Outlets [Re: andey]
sedesigner1 Offline
Member
Registered: 04/05/13
Posts: 22
Loc: NJ
I think we all have stories of what the customer has plugged into outlets after we've left. That's why you're only responsible up to and including the device.
Greg
Top
#214784 - 01/24/15 08:18 AM Re: Understanding NEMA 5-15 / 5-20 Outlets [Re: andey]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Just figured that out, did you?

Now, take a look at the cords with multiple outlets - cords that are only #16 wire ... even a single 15 amp appliance has that cord overloaded.

Look inside one of those outlet strips with integral 15 amp breakers, and you'll find the internal wire is best described as 'dental floss gauge.'

If household wiring followed the same voltage drop advice as we are given for using extension cords, we'd wire houses in #8.

When reality conflicts with theory ... and everything is working fine ... it's the theory, the basic assumptions, that need to be reconsidered.
Top
#214815 - 01/27/15 01:16 PM Re: Understanding NEMA 5-15 / 5-20 Outlets [Re: andey]
sedesigner1 Offline
Member
Registered: 04/05/13
Posts: 22
Loc: NJ
When I mentioned what customers plug in, I had a specific case in mind. Home owner had 3 outlets in a small room and wanted a 4th. Not to worry, they bought a 6', #16 extension cord and stapled it to the wall, and plugged in a floor lamp. Then they wanted a closet light. Not to worry, they bought a 2nd #16 extension cord and plugged it into the first, drilled a hole into the closet and again stapled everything in place. Oops, how to connect the light (pull chain fixture)? They cut the 2nd extension cord and hardwired the fixture, and mounted the fixture directly to an exposed wood beam (who needs a box). They told me "it's only 2 lights so it's not overloaded". I was speechless.
Top
#214816 - 01/27/15 01:46 PM Re: Understanding NEMA 5-15 / 5-20 Outlets [Re: andey]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6833
Loc: Brick, NJ USA
OK, time for a stroll down Memory Lane...
Back in time installation of 'outlets' using zip cord, stapled to baseboards and thru walls was common. Matter of fact, Eagle/Leviton made 'devices' for 'surface wiring'.

The device was wired; forget polarity & that 'ground', Screwed to the baseboard, and extended where 'outlets' were wanted. Some installs were 'tapped' off of a duplex, not plugged in.

Light fixtures were installed like Sedesigner1 describes.

Those were the days!! ??
_________________________
John
Top
#214817 - 01/27/15 02:41 PM Re: Understanding NEMA 5-15 / 5-20 Outlets [Re: andey]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
This was the closet light in my daughter's new house when I first saw it. The "home inspector" either missed it or thought it was fine. No switch, you just plugged the cord to an extension cord through the wall from the other room, hanging by the door.
(yeah I fixed it)

_________________________
Greg Fretwell
Top
#214836 - 01/29/15 01:04 PM Re: Understanding NEMA 5-15 / 5-20 Outlets [Re: andey]
sedesigner1 Offline
Member
Registered: 04/05/13
Posts: 22
Loc: NJ
Nice! I especially like the cable support and service loop. Is that a water pipe at lower right? Even better!
Top
#214837 - 01/29/15 01:10 PM Re: Understanding NEMA 5-15 / 5-20 Outlets [Re: andey]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
Oh yeah, That goes to the water heater

_________________________
Greg Fretwell
Top
#214838 - 01/29/15 02:37 PM Re: Understanding NEMA 5-15 / 5-20 Outlets [Re: andey]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6833
Loc: Brick, NJ USA
I guess you can plug in a water heater?

_________________________
John
Top
Page 1 of 3 1 2 3 >

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
0 registered (), 66 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals