#214759 - 01/22/15 10:40 AM Conduit fitting question
sedesigner1 Offline
Member
Registered: 04/05/13
Posts: 22
Loc: NJ
We are installing a new oil filled transformer and will be penetrating the oil pit liner. The drawings indicate the conduit immediately turning up to a field termination cabinet. The conduit is 4" sch 40 PVC, the cable will be 3-1/C 350kcmil. The engineer says the conduit needs to penetrate the liner at a right angle and to use a 90 degree LB fitting to turn up as we don't have room for a sweep. As this will later be filled with stone, is it acceptable to use an LB fitting that will be below grade? I've never done this before, but am drawing a blank if it's permissible. Thanks for any input. Greg
Top
Work Gear for Electricians and the Trades
#214760 - 01/22/15 11:57 AM Re: Conduit fitting question [Re: sedesigner1]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Not Permitted. You must retain access to that LB when installation is complete, just as if it were a junction box.

Invariably, someone at this point will say "but we can remove the stones later." They might even find code language that would allow, say, minor amounts of leaf mulch to conceal outdoor lighting fittings. Nice try; we might as well just eliminate any restrictions on accessibility if we're going to stretch that loophole that far.

You'd be better using another code provision that might let you re-examine 'conduit fill,' and make a sweep using a conduit barely large enough for the cable to enter. Or, for that matter, use a cable that's rated for direct burial.
Top
#214761 - 01/22/15 12:19 PM Re: Conduit fitting question [Re: renosteinke]
sedesigner1 Offline
Member
Registered: 04/05/13
Posts: 22
Loc: NJ
Renosteinke, thanks for the quick response. That's what I thought, treat the LB like a junction box, you need to retain access. I told the engineer, and he agreed to look for a different solution. I appreciate the quick input. Best regards, Greg
Top
#214762 - 01/22/15 12:39 PM Re: Conduit fitting question [Re: sedesigner1]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
You may consider a 'Quazite' box adjacent to the pit; punch thru the sidewall of the box into the pit and exit at 90 degrees either right or left side & up.

The LB would be a red tag.



_________________________
John
Top
#214764 - 01/22/15 03:36 PM Re: Conduit fitting question [Re: sedesigner1]
sedesigner1 Offline
Member
Registered: 04/05/13
Posts: 22
Loc: NJ
John, I'm having a hard time picturing your solution. I guess I'm missing something in the translation. Could you further explain? We've put this on hold so I have some time to complete.
Thanks, Greg
Top
#214765 - 01/22/15 05:43 PM Re: Conduit fitting question [Re: sedesigner1]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
OK, I'll try...
A 4" nipple out of the side of the pit, and into the side of a 'quazite' box of suitable depth and bending spaces for your conductors.

Basically think like a j-box adjacent to the tranny pit. Then exit the 'box' from either side to your cabinet.

_________________________
John
Top
#214766 - 01/22/15 06:09 PM Re: Conduit fitting question [Re: sedesigner1]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Another bit of code trivia:

The accessibility requirement for the LB would also apply to a 90 degree fitting for "Flex" or "Sealtite." The requirement does not apply, however, to MC. "MC" is best described as flex that is sold with the wires already in it.

Whether there is a rated MC and fitting for your application is another question.
Top
#214767 - 01/22/15 06:45 PM Re: Conduit fitting question [Re: sedesigner1]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
I've seen MC that was suitable for under slab and concrete encasement, it had/has a PVC exterior jacket, and special connectors.

There could be an issue with bend radius.

This may be an idea, but...availability?? minimum length??
Is it 'made to order', or warehouse stock?

I only saw it on one job, at least 5-8 years back.

_________________________
John
Top
#214772 - 01/22/15 09:20 PM Re: Conduit fitting question [Re: sedesigner1]
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Southwire's current price sheet lists it's PVC coated MC cable at $79.80 a foot for 3-350kcm with a ground


Top
#214776 - 01/23/15 06:57 AM Re: Conduit fitting question [Re: sedesigner1]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
Thanks Electure, this may help the OP.

100' minimum????? $7980.00 plus any tax???

Curious
_________________________
John
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 04/03/02
Posts: 6778
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 70 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals