The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
breaker meltdown
by sparky
Yesterday at 07:30 PM
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 10
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 263 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#214757 - 01/21/15 09:59 AM Wall Mounted Oven 4.1KW
SparksFlying Offline
New Member

Registered: 10/17/14
Posts: 7
Loc: Austin, Texas
What size breaker and what size cable should be used.

Top
#214758 - 01/21/15 01:48 PM Re: Wall Mounted Oven 4.1KW [Re: SparksFlying]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
Sounds like 10ga/30a to me. What do the instructions say?
A lot of times they say 8ga/40a no matter what oven is installed.
_________________________
Greg Fretwell

Top
#214786 - 01/24/15 09:24 AM Re: Wall Mounted Oven 4.1KW [Re: SparksFlying]
Scott35 Offline

Broom Pusher and
Member

Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
4100 VA / 240V = 17.0833333- Amps

As Greg has mentioned, #8 THHN CU. protected by a 40 Amp 2 Pole Breaker is "The Norm".

--Scott (EE)
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Top
#214791 - 01/24/15 11:45 AM Re: Wall Mounted Oven 4.1KW [Re: SparksFlying]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
It would probably live forever on 12ga and 20a breaker, even with the timer and the light inside but you should still be sizing at 125% of the calculated current. That is how I got to 10ga/30a.
_________________________
Greg Fretwell

Top
#214812 - 01/26/15 11:49 AM Re: Wall Mounted Oven 4.1KW [Re: SparksFlying]
SparksFlying Offline
New Member

Registered: 10/17/14
Posts: 7
Loc: Austin, Texas
Yes they only call for a 20ga and 20amp breaker but we are going with a 10ga/30amp and sleep well...'

Thanks