The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 10
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
1 registered (geoff in UK), 202 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#214635 - 12/29/14 03:39 PM NM wire in commercial ceiling?
Trick440 Offline
Member

Registered: 08/15/05
Posts: 248
Loc: Waterford, MI, USA
Can NM wire be used in a commercial building?

We have a suspended ceiling, that is going to be drywalled. Its steel framing and grid.

I just had 2 guys on a job working today and they ran NM for the recessed lighting?! They even fished it down a steel framed wall to the switch.

The Journeymen on site was assuring me its legal, cause its being drywalled and its not a 3 story building?

I have never tried running NM in commercial and never looked it up, but... Looking up 334.12, uses not permitted, (a)(2) says not permitted in, dropped or suspended ceilings.

Please confirm that these guys just wasted more than half a day doing it wrong. smile


Edited by Trick440 (12/29/14 03:42 PM)
_________________________
Shake n Bake

Top
2014 / 2011 NEC & Related Books and Study Guides
#214636 - 12/29/14 05:04 PM Re: NM wire in commercial ceiling? [Re: Trick440]
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
Depends on the construction type. Section 334.10(3) allows NM in type III, IV an V constructed buildings when concealed with a 15 minute fire rated assembly.

A dropped ceiling that is drywalled is different than a accessible grid type drop ceiling...