#214573 - 12/22/14 10:42 AM Single Pole Control Switch On 240-v Motor
02vito Offline
New Member
Registered: 12/22/14
Posts: 2
Loc: CO
Installed a 20-a, 240-v, single-phase, dedicated branch circuit for an automotive lift.

The lift-installation instructions required that the lift-motor supply voltage (under load)and current be measured and recorded.

In doing this, we noticed that the lift-motor control switch is only a single-pole device. Other lifts we have worked on have had 2-pole switches.

We were surprised that a nationally-known, ETL-listed lift would use a single-pole switch on a 240-v device. Our local electrical inspector was also surprised when we informed him of what we found.

I'm wondering what others are seeing in this type application. I don't recall ever seeing a 240-v device operated from a single-pole control.
Top
2017 / 2014 NEC & Related Books and Study Guides
#214575 - 12/22/14 11:38 AM Re: Single Pole Control Switch On 240-v Motor [Re: 02vito]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
You can use single pole "control" but you still need a 2 pole disconnect.

Quote:
430.84 Need Not Open All Conductors.
The controller shall not be required to open all conductors to the motor.
Exception: Where the controller serves also as a disconnecting means, it shall open all ungrounded conductors to the motor as provided in 430.111.
_________________________
Greg Fretwell
Top
#214582 - 12/22/14 11:49 PM Re: Single Pole Control Switch On 240-v Motor [Re: 02vito]
NORCAL Offline
Member
Registered: 09/25/02
Posts: 865
HVAC equipment uses single pole contactors for 208-240V units & 2 pole ones for 3 units all the time.

As the code section quoted in the previous post shows, it's quite code compliant, but means any electrician needs to be on their toes & trust nothing.
Top
#214603 - 12/24/14 11:45 AM Re: Single Pole Control Switch On 240-v Motor [Re: 02vito]
02vito Offline
New Member
Registered: 12/22/14
Posts: 2
Loc: CO
Thank you both for your responses.

The circuit in question has of course a 2-pole breaker. The lift was furnished with a pigtail and twist-lock plug, so that serves as the local disconnect.

Most of my experience is in the power industry, and at the utility where I worked, we always used control devices that broke all hot circuit legs.
Top
#214607 - 12/24/14 06:17 PM Re: Single Pole Control Switch On 240-v Motor [Re: 02vito]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
Breaking all ungrounded legs is actually pretty uncommon when they use solid state switching for controls.
_________________________
Greg Fretwell
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (sparkyinak), 44 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals