The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
breaker meltdown
by sparky
09/27/16 07:30 PM
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 10
sparky66wv 8
gfretwell 8
Vlado 6
Who's Online
0 registered (), 295 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#214573 - 12/22/14 10:42 AM Single Pole Control Switch On 240-v Motor
02vito Offline
New Member

Registered: 12/22/14
Posts: 2
Loc: CO
Installed a 20-a, 240-v, single-phase, dedicated branch circuit for an automotive lift.

The lift-installation instructions required that the lift-motor supply voltage (under load)and current be measured and recorded.

In doing this, we noticed that the lift-motor control switch is only a single-pole device. Other lifts we have worked on have had 2-pole switches.

We were surprised that a nationally-known, ETL-listed lift would use a single-pole switch on a 240-v device. Our local electrical inspector was also surprised when we informed him of what we found.

I'm wondering what others are seeing in this type application. I don't recall ever seeing a 240-v device operated from a single-pole control.

Top
2014 / 2011 NEC & Related Books and Study Guides
#214575 - 12/22/14 11:38 AM Re: Single Pole Control Switch On 240-v Motor [Re: 02vito]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
You can use single pole "control" but you still need a 2 pole disconnect.

Quote:
430.84 Need Not Open All Conductors.
The controller shall not be required to open all conductors to the motor.
Exception: Where the controller serves also as a disconnecting means, it shall open all ungrounded conductors to the motor as provided in 430.111.
_________________________
Greg Fretwell

Top
#214582 - 12/22/14 11:49 PM Re: Single Pole Control Switch On 240-v Motor [Re: 02vito]
NORCAL Offline
Member

Registered: 09/25/02
Posts: 805
HVAC equipment uses single pole contactors for 208-240V units & 2 pole ones for 3 units all the time.

As the code section quoted in the previous post shows, it's quite code compliant, but means any electrician needs to be on their toes & trust nothing.

Top
#214603 - 12/24/14 11:45 AM Re: Single Pole Control Switch On 240-v Motor [Re: 02vito]
02vito Offline
New Member

Registered: 12/22/14
Posts: 2
Loc: CO
Thank you both for your responses.

The circuit in question has of course a 2-pole breaker. The lift was furnished with a pigtail and twist-lock plug, so that serves as the local disconnect.

Most of my experience is in the power industry, and at the utility where I worked, we always used control devices that broke all hot circuit legs.

Top
#214607 - 12/24/14 06:17 PM Re: Single Pole Control Switch On 240-v Motor [Re: 02vito]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
Breaking all ungrounded legs is actually pretty uncommon when they use solid state switching for controls.
_________________________
Greg Fretwell

Top