The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
Yesterday at 09:33 AM
breaker meltdown
by crselectric
Yesterday at 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 17
gfretwell 9
sparky 9
sparky66wv 8
Vlado 6
Who's Online
1 registered (gfretwell), 258 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#214531 - 12/18/14 07:28 PM derating rooftop conductors
BigB Offline
Member

Registered: 03/31/04
Posts: 725
Loc: Tucson, AZ USA
When derating THWN-2 copper conductors for ambient that will eventually terminate in a sub panel with a 125 amp rating can I use the 90C column?

Top
2014 / 2011 NEC & Related Books and Study Guides
#214533 - 12/19/14 12:54 AM Re: derating rooftop conductors [Re: BigB]
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
The sole and only reason for that column IS derating.

For there are no 90 degree rated devices out there.

One then uses the lesser computed ampacity limit.

So, yes, you start with the 90 degree column.