The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
2 registered (Radar, LongRunner), 224 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#214341 - 11/18/14 09:14 AM Whirlpool tub grounding with pex
yzman720 Offline
New Member

Registered: 11/05/14
Posts: 2
Loc: missouri
We have a new construction home that I am installing a whirlpool tub in. I have ran a 12/2 with ground dedicated circuit that will have a gfi on the outlet that the tub will plug into. My questions are:

1. The entire house is ran in pex what do I ground the motor ground lug to on the motor itself?

2. The directions say "The circuit must be a (3) wire circuit from the electrical supply panel. A grounded neutral wire and a third wire, earth ground, are essential."
Is this what I already have with the 12/2 with ground? The wording of that confuses me for some reason.

If it matters the home has no uffer ground, only 2 ground rods will be installed.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#214342 - 11/18/14 10:05 AM Re: Whirlpool tub grounding with pex [Re: yzman720]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
To be clear, we are talking about a hydro massage bath tub, not a spa?

If there is no metal around the tub anywhere that needs to be bonded, you may not be using that lug. This is not to connect the pump to the grounding system or any electrode. It is only for equipotential bonding of all conductive parts in the vicinity of the tub.
_________________________
Greg Fretwell

Top
#214344 - 11/18/14 01:30 PM Re: Whirlpool tub grounding with pex [Re: yzman720]
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
1) A properly functioning GFCI receptacle is going to be protection.

2) But GFCI's -- especially exposed to the elements -- fail all of the time. That's why one is expected to test them at least once a month.

3) If the GFCI has failed then there is a small, non-zero, risk that the insulation within the motor could breakdown.

4) Due to human sweat, every tub or spa gradually becomes salty -- and quite conductive.

5) The very act of pumping a conducting fluid through an electric field induces a current -- and voltage. This happens even if everything is totally squared away. Very few tub designs shield the circulating water from this effect. [Faraday discovered it, BTW.]

6) Consequently one is well advised to bond every hot tub/ spa to ground with any factory supplied lug. It almost certainly is doing double duty: bleeding off induced voltage (per 5) and providing a back-up short circuit path back to the panel, lest the GFCI fail in use.

The way this is done in elevator pits (notoriously wet) is that a bonding conductor (green) is wirenutted inside a nearby junction box (W/P, Bell box) and brought out to the equipment lug. Depending upon the circumstances, this whip can be naked (a forgiving situation) or enclosed in a raceway for protection from physical damage.

BTW the voltage effect can build and build. I've tested waters that had reached 45 VDC above the local ground voltage. Every time anyone exited the tub, they got a jolt to their groin. A trivial bonding run cured the problem in no time.

BTW, the national 'help' line for the manufacturer was totally unaware of the physics of their product: not a clue.

Their design had no mechanism for bleeding off the induced charge. (It was building up like a gigantic Leyden jar.)

http://www.instructables.com/id/Make-A-Water-Leyden-Jar/



Edited by Tesla (11/18/14 01:32 PM)
_________________________
Tesla

Top
#214345 - 11/18/14 01:37 PM Re: Whirlpool tub grounding with pex [Re: yzman720]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
The code specifically says the equipotential bonding is not connected to the electrodes but it always will be, simply by the construction of the equipment.
A plastic tub, connected with plastic pipe, no heater and no metal nearby leaves very little to bond.
_________________________
Greg Fretwell

Top
#214350 - 11/19/14 03:14 AM Re: Whirlpool tub grounding with pex [Re: yzman720]
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
Exactly.

My B-i-L had EXACTLY such a hot tub.

In pretty short order, he -- and family -- were being shocked something fierce. (45 Volts measured, Fluke meter.)

A draining ground eliminated all hazards.

Check out my link.

The NEC has missed this: human sweat = salty water.

As time goes by, the salt concentration only goes UP.

You end up with a salt-water Leyden jar.

The BETTER the insulation/ non-conduction -- the more extreme the voltage can build.

Yeap. It can get to alarming thresholds.

It's commented upon time and again. The link to the physics is lost.

Everyone thinks that the induced voltage is either a phantom or a loose wire.

Nope!


Edited by Tesla (11/19/14 03:17 AM)
_________________________
Tesla

Top
#214356 - 11/19/14 07:50 AM Re: Whirlpool tub grounding with pex [Re: yzman720]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Hence, the requirement to 'bond the water'.
_________________________
John

Top
#214358 - 11/19/14 11:13 AM Re: Whirlpool tub grounding with pex [Re: yzman720]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
I am still not sure what kind of tub we are talking about here. If it is just a jetted bath tub, the bond the water requirement is not there, at least not in the 2011 (680 part VII). You are also not bonding the tile floor. You do bond all existing metal parts in contact with the water but you do not need to add a bonding fitting if it is not there. There is no part of the motor shaft exposed to the water in the pump. If the plumbing is plastic and no heater, I am not sure how you bond the water.
Obviously if this is a "spa", we get a lot more serious about it and the hazards are virtually identical.
_________________________
Greg Fretwell

Top
#214360 - 11/19/14 04:26 PM Re: Whirlpool tub grounding with pex [Re: yzman720]
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
In case I've not been clear: the water in the tub, itself, is a conductor.

No existing design totally protects the pumped water from the magnetic field generated by the pump motor.

It's counter-intuitive, but even an AC motor produces a DC bias in its field. (See Buss and the short circuit fault calculations in Ugly's.) This is due to the material physics of the steel. No motor/ transformer steel is ever cast/ rolled without a bias in its magnetic grain.

The energy bleed/ pump from this effect is trivial. However, as a Leyden jar, the energy simply builds and builds -- hour after hour.

It doesn't kill anyone: it just gives them a very painful jolt as they step out of the salt bath and onto the very grounded exterior world.

And, yes, the manufacturers (and NEC) have totally missed this effect.

I have tested its voltage in the real world. This is the source of COUNTLESS phantom voltage service calls that befuddle electricians across the land. They keep looking for METALLIC conductors as the source of the voltage.

They fail to recognize that the circulating salt water has become a Separately Derived Service -- a Leyden jar of a huge scale.

Visit the link up top to get an idea of the physics.

The hot tub/ spa may start out as fresh, potable water. It does not stay that way with sweaty human users. The salt can never boil out/ evaporate from the solution. It starts out trivially low, and proceeds to build and build.

Without a doubt, these tubs were tested with fresh, pure, water. It is not a conductor, and will not create the Leyden jar effect.

ALL of the current designs on the market have this conceptual flaw. They all need to have a metallic bond running through to the water -- taking the voltage back down to the local equipotential plane.

When this is done, the problem entirely goes away. The actual energy stored by these Leyden jars is trivial. It's just that no-one enjoys discharging it through their groin, which is where the sensation is the most intense.

It gets bad enough that owners stop using their hot tubs. This is why you see so many units scarcely being used.

It's a rare individual that admits they're getting so jolted. I had to experience it myself. Then, when queried, everyone admitted it had happened to them, too. It was simply too personal to bring up in conversation.

So don't be surprised if troubled customers don't broach the topic, either. It's taboo. It's also a real problem faced by millions.

It's ironic: the entire industry has designed spas to have zero conduction between the water in the tub and the outside world. It turns out that's THE problem.

A trivial #12 bare wire from water to the Service ground solves everything. Poof, the problem is gone.

You can stop chasing your tail hunting for the phantom voltage source.
_________________________
Tesla

Top
#214363 - 11/19/14 11:08 PM Re: Whirlpool tub grounding with pex [Re: yzman720]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
The problem you are talking about will affect hot tubs and spas where the water is not usually changed very often but a jetted bathtub, usually gets fresh water every time. That is probably why they are exempt from the water bonding requirements.
_________________________
Greg Fretwell

Top
#214367 - 11/20/14 05:59 PM Re: Whirlpool tub grounding with pex [Re: yzman720]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Nice theory, Tesla, except for one thing ....

The proposals that led to the equipotential bonding plane requirements were based on some issues that arose in Las Vegas- in FRESH water pools. No such (voltage gradient) problems were found in the also popular salt water pools.