The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
breaker meltdown
by crselectric
09/24/16 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 15
sparky 9
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 292 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#214208 - 10/28/14 03:54 PM Residue on wires in panel box??
JoeJoeB Offline
New Member

Registered: 10/12/14
Posts: 4
Loc: Boston, MA
Looking for some feedback please. I noticed an oil-like residue on some branch wires and breakers inside a panel box today, and I wondering if anyone knows what this might have been. It was actually dripping in places. Don't think it was water.
Thx-Joe


Edited by JoeJoeB (10/28/14 03:56 PM)

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#214209 - 10/28/14 04:55 PM Re: Residue on wires in panel box?? [Re: JoeJoeB]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
Visual of the top of the panel; outside where the cables enter.

IMHO, a qualified electrical contractor should check this out.
_________________________
John

Top
#214210 - 10/28/14 05:56 PM Re: Residue on wires in panel box?? [Re: HotLine1]
JoeJoeB Offline
New Member

Registered: 10/12/14
Posts: 4
Loc: Boston, MA
It's all sealed up. Putty looks fresh though. I'm already calling in electrician for other issues as well.


Edited by JoeJoeB (10/28/14 05:58 PM)

Top
#214231 - 10/31/14 07:50 AM Re: Residue on wires in panel box?? [Re: JoeJoeB]
andey Offline
Member

Registered: 08/05/08
Posts: 29
Loc: germany
JoeJoe, I have seen this before serveral times.
If you are sure it didnt come from the outside, I would say it is plasticiser (DINP, DEHP etc) coming out of the PVC insulation. It's a quality problem from the wire manufacturer that makes it dissolve from the PVC.

It looks like a thin film of oil and can be so much that you see drops hanging from the wires.
The inuslation will eventually harden and lose its breakdown specifications.
You should perform insulation measuring on the site and think about replacing the wiring if values are bad or it looks to messy.

Top
#214234 - 10/31/14 09:22 AM Re: Residue on wires in panel box?? [Re: JoeJoeB]
Texas_Ranger Offline
Member

Registered: 12/17/01
Posts: 2331
Loc: Vienna, Austria
There are a few interesting effects. One is that the copper conductor is discoloured (oxydised) even in relatively new wire. The process is known to the manufacturers and considered harmless if the conductors are cleaned before they are terminated. I have seen affected wires from ca. 1960 that were still fine electrically and mechanically.

Only in one case the corrosion was severe enough to cause problems, the moulded trailing socket of a late-1950s extension lead actually covered the pins of an inserted plug with green slime. I never bothered to measure contact resistance but I'm convinced it would be far too high.

Top
#214238 - 10/31/14 09:09 PM Re: Residue on wires in panel box?? [Re: Texas_Ranger]
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8530
Loc: SI,New Zealand
Yup,
Plasticiser, is what that is.
We had a problem over here with the earlier PVC cables installed in the 60's and 70's.
My boss when I was an apprentice got some in his eye (why you'd rub your eye with that on your fingers, I have no idea, but there you go.) grin
It's like oil, because PVC itself is made from petroleum products.
I once had some pictures of this stuff (it was coloured green here, because it was corroding the bare earth wire in the cables) running out of the earth slot of a socket-outlet here and down the wall, it gets worse during the summer months when wall temperatures are higher.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#214242 - 11/01/14 07:09 AM Re: Residue on wires in panel box?? [Re: JoeJoeB]
Texas_Ranger Offline
Member

Registered: 12/17/01
Posts: 2331
Loc: Vienna, Austria
I've read somewhere online that the same thing (green goo dripping out of sockets) happened in the UK as well. As I said I've had that happened with a very old extension lead (must have been one of the first designs using moulded plugs and trailing sockets). All other instances were rather harmless, the conductor surface was slightly discoloured (the typical brown of copper oxide) but cleaned up nicely and existing connections did not show any impedance issues, in spite of being over 50 years old in some instances.

Top
#214250 - 11/03/14 02:04 PM Re: Residue on wires in panel box?? [Re: JoeJoeB]
JBD Offline
Member

Registered: 07/12/01
Posts: 599
Loc: WI, USA

Top
#214258 - 11/04/14 07:42 AM Re: Residue on wires in panel box?? [Re: JoeJoeB]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
Thank you JBD!!
_________________________
John

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals