The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 8
Trumpy 6
Who's Online
0 registered (), 192 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#214169 - 10/20/14 03:22 AM Inverter/Charger advice
OJazem Offline
New Member

Registered: 10/19/14
Posts: 1
Loc: Yemen
I don't know if this is the right place to post about inverters. If not, please advice.

I want to make a backup plan for my gaming consoles that runs for at less 5 hours using inverter/charger and maintenance free batteries. I will be connecting PS4(150 watt approx.) or ps3(100 watt approx.) + LED TV(110 watt approx) + 5 LED lights.

What I am planning to have is an inverter/charger (2000 watt) with two maintenance free batteries (150 Amps each).

Is this enough to run 5 hours?? and how much time will it take to be fully charged??
Please advice if there is a better solution. Am new at this, so please be patient. And thanks in advance.

Top
Green Building & Alternative Energy Related:

Green Building, Projects & Technology, Alternative & Renewable Energy and Efficiency Books and Reference Materials
Green Bldg, Projects & Technology, Alternative & Renewable Energy Books & References

#214172 - 10/20/14 11:29 AM Re: Inverter/Charger advice [Re: OJazem]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Theoretically it looks good but YMMV
300 A/H of battery @ 12v = 3.6KVA
300 watt hours of load x 5 = 1.5KVA


I have never seen one of these UPS deals that actually approached the theoretical time they should run. There is some loss in the inverter and you really need to know what the discharge rate was used to get the 150 A/H for the battery
_________________________
Greg Fretwell

Top
#214178 - 10/21/14 06:44 PM Re: Inverter/Charger advice [Re: gfretwell]
LarryC Offline
Member

Registered: 07/05/04
Posts: 776
Loc: Winchester, NH, US
Battery Amp-Hour ratings are usually determined by the 20 hour discharge curve.

I believe for a 5 hour discharge, you should derate to 70%.

You may want to set up the UPS with the intended load and measure the actual current draw of the system.