#214139 - 10/12/14 07:30 PM Daisy chaining on 2pole 30 amp breaker??
JoeJoeB Offline
New Member
Registered: 10/12/14
Posts: 4
Loc: Boston, MA
Hello, I'd like some input from licensed electricians in MA please.
I'm a home inspector and I have a builder who wants to install 2 4-wire 30amp outlets on a single 30amp double-pole breaker in a detached garage workshop (arc weld,etc.). Not being a licensed electrician, I can't site the actual code on this one, but my gut is that it's better off being 2 separate circuits. The owner claims that due to his needs he would never be running both at same time. I say, what about the next guy who buys the house who has different plans?
Are these outlets even really engineered to be daisy chained?
Also, even if they were pig-tailed in a separate j-box, the argument that they're protected against overload by the breaker tripping seems weak. I see a tripping breaker as a last line of defense against fire, not something I really want to rely on if I can help it. I've seen so many corroded breakers that don't trip when needed.
What do you guys think? Is there an actual code that says you can or cannot do? Or is this up to the local electrical inspector.
Thx- Joe
Top
Work Gear for Electricians and the Trades
#214140 - 10/12/14 08:54 PM Re: Daisy chaining on 2pole 30 amp breaker?? [Re: JoeJoeB]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Are they feeding 2 receptacles? If so, you are not going to find anything.
_________________________
Greg Fretwell
Top
#214141 - 10/12/14 10:26 PM Re: Daisy chaining on 2pole 30 amp breaker?? [Re: JoeJoeB]
Tesla Offline
Member
Registered: 06/16/04
Posts: 1273
Loc: Sacramento, CA
He's good to go -- as long as he's using 30A outlets.



_________________________
Tesla
Top
#214143 - 10/13/14 09:50 AM Re: Daisy chaining on 2pole 30 amp breaker?? [Re: JoeJoeB]
ghost307 Offline
Member
Registered: 05/09/05
Posts: 900
Loc: Chicago Illinois USA
Absolutely not a problem as long as he uses 10 AWG wire (or larger).

There's no difference between this and allowing more than a single 15A receptacle on a 15A breaker.

If the next guy tries to use both at the same time the breaker will protect things; the same way that the 15A breaker would react to someone running his PC, printer, router, TV, videogame, Xmas tree lights and a bunch of chargers off of a single receptacle in the living room.
_________________________
Ghost307
Top
#214144 - 10/13/14 12:15 PM Re: Daisy chaining on 2pole 30 amp breaker?? [Re: JoeJoeB]
JoeJoeB Offline
New Member
Registered: 10/12/14
Posts: 4
Loc: Boston, MA
Appreciate the feedback!
Top
#214145 - 10/13/14 12:22 PM Re: Daisy chaining on 2pole 30 amp breaker?? [Re: JoeJoeB]
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
It all depends which Code it's under.

It's OK by the NEC.

The IRC however, prohibits multiple receptacles on circuits over 20 Amps
Top
#214146 - 10/13/14 06:30 PM Re: Daisy chaining on 2pole 30 amp breaker?? [Re: JoeJoeB]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Interesting Scott.
Florida did not pick up the IRC electrical articles, simply adopting the NEC, pretty much unaltered. There are only a couple of changes. (adding bonding metal studs and removing the GFCI requirement on some hardwired pool pumps).
Top
#214148 - 10/14/14 11:22 AM Re: Daisy chaining on 2pole 30 amp breaker?? [Re: ghost307]
Texas_Ranger Offline
Member
Registered: 12/17/01
Posts: 2391
Loc: Vienna, Austria
Originally Posted By ghost307
Absolutely not a problem as long as he uses 10 AWG wire (or larger).

There's no difference between this and allowing more than a single 15A receptacle on a 15A breaker.

If the next guy tries to use both at the same time the breaker will protect things; the same way that the 15A breaker would react to someone running his PC, printer, router, TV, videogame, Xmas tree lights and a bunch of chargers off of a single receptacle in the living room.

Make that a laser printer and add a coffee pot or space heater and you're getting there. All the other gadgets are in the lower double-digit watt range and awfully unlikely to trip a breaker.
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6778
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (HotLine1), 61 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals