The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Correct rotation, wrong sequence
by Potseal
Today at 03:14 PM
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
HotLine1 10
Potseal 9
sparkyinak 8
Texas_Ranger 7
Who's Online
0 registered (), 198 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#214048 - 09/25/14 11:21 PM Water tank de-icer - panel is 500-600' from tank
Potseal Offline
Member

Registered: 02/23/13
Posts: 200
Loc: Saskatchewan
I was asked today about the requirements for powering a 1500W 120V livestock water tank de-icer that was 500-600ft away from the panel. First thought that came to mind was "sub-panel". At that distance is it even reasonable to run conductors straight to the heater? At 500' and using a 3% voltage drop I ended up with #4 Cu (75 degree Celcius column Table 2 CEC). Wouldn't a small sub-panel placed closer to the tank and then running smaller gauge conductors to the heater be a better idea?
_________________________
A malfunction at the junction

Top
2014 / 2011 NEC & Related Books and Study Guides
#214051 - 09/26/14 06:44 AM Re: Water tank de-icer - panel is 500-600' from tank [Re: Potseal]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6805
Loc: Brick, NJ USA
Potseal:

Vd for the load in the subpanel would be equal to what you calc'd for just the load.

IF you ran 3 wire & grd to the sub, you would have available 'load' capacity at the area.

Depending on available voltages at a source, 480 volt to the location, and a small 480-120 transformer may be economical.
_________________________
John

Top
#214053 - 09/26/14 10:52 AM Re: Water tank de-icer - panel is 500-600' from tank [Re: Potseal]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Potseal, you are under a misconception.

What limits voltage drop issues to branch conductors alone? Circuit or panel - you need to allow for voltage drop. Only a higher voltage will lessen your voltage drop.

Set the 'percentage rule' aside for the moment. What's your final voltage when the heater is in use? If your incoming voltage is on the high side (127V is not all that rare), then you could very easily have a very acceptable 118V at the heater.

Whether you should set a panel is another question. I'm biased in favor, for two reasons.
First, I like having an OCPD, GFCI, and disconnecting means close to the point of use.
Second, you almost always have a later desire to add a light, a service receptacle, whatever in the same area. Might as well pull a 4th wire and have a second circuit.

Run big pipe - pipe is cheap - and you can pull bigger wire later if you need it.

Finally ...don't have 480? Make it. Just use two transformers: one 'up' and one 'down.'

Top
#214056 - 09/26/14 01:45 PM Re: Water tank de-icer - panel is 500-600' from tank [Re: Potseal]
Potseal Offline
Member

Registered: 02/23/13
Posts: 200
Loc: Saskatchewan
Thank-you for the suggestions. I will definitely consider them as it could solve the distance issue.

FYI

After doing my own calculations I decided to look online to see if I could compare my results to other available information. Found this related chart as a result:

_________________________
A malfunction at the junction