The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Webmaster
Today at 12:03 AM
Re: Fabricating Guards out of Lexan?
by frank
Yesterday at 04:11 PM
Would ELV branch circuits be a good idea?
by gfretwell
Yesterday at 01:26 PM
Why cables look like they do
by Texas_Ranger
Yesterday at 12:33 PM
100% breakers?
by Texas_Ranger
01/16/17 06:13 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 20
HotLine1 19
gfretwell 13
Trumpy 12
ghost307 12
Who's Online
1 registered (Webmaster), 0 Guests and 64 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#214000 - 09/18/14 02:54 PM fire pump service disconnect
cgw Offline
Member

Registered: 07/29/04
Posts: 133
Loc: Rochester NY
Is it OK to have a fire pump main service disconnect then feeder to the fire pump controller which has it's own disconnect?
Too many disconnects.
In this case the fire pump is far from the electric service (>350'). The fire pump service entrance could be run all the way to the fire pump room. However the standby generator is located at the electric service so it makes much more sense to put the main disconnect and transfer switch near the electric service (and generator) and run a feeder to the fire pump controller.

Top
2017 / 2014 NEC & Related Books and Study Guides
#214002 - 09/19/14 07:01 AM Re: fire pump service disconnect [Re: cgw]
HotLine1 Offline


Member

Registered: 04/03/02
Posts: 6829
Loc: Brick, NJ USA
It will be best to check with the design professional for the project, and the local AHJs, both Electrical and Fire

Read thru 695.4 (B) (1). IMHO, there are too many variables to say yes or no to your situation.
_________________________
John

Top
#214005 - 09/20/14 06:45 AM Re: fire pump service disconnect [Re: cgw]
JBD Offline
Member

Registered: 07/12/01
Posts: 599
Loc: WI, USA
I see nothing in the NEC that would prevent you from having two disconnects, in series, for a fire pump installation.
I have designed, and had installed, new disconnects with short circuit protection upstream from existing fire pump services. They have not been questioned by the AHJ.

Top


ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals