Is it OK to have a fire pump main service disconnect then feeder to the fire pump controller which has it's own disconnect?
Too many disconnects.
In this case the fire pump is far from the electric service (>350'). The fire pump service entrance could be run all the way to the fire pump room. However the standby generator is located at the electric service so it makes much more sense to put the main disconnect and transfer switch near the electric service (and generator) and run a feeder to the fire pump controller.
Top
2017 / 2014 NEC & Related Books and Study Guides
#214002 - 09/19/14 07:01 AM Re: fire pump service disconnect [Re: cgw]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
It will be best to check with the design professional for the project, and the local AHJs, both Electrical and Fire

Read thru 695.4 (B) (1). IMHO, there are too many variables to say yes or no to your situation.

_________________________
John
Top
#214005 - 09/20/14 06:45 AM Re: fire pump service disconnect [Re: cgw]
JBD Offline
Member
Registered: 07/12/01
Posts: 599
Loc: WI, USA
I see nothing in the NEC that would prevent you from having two disconnects, in series, for a fire pump installation.
I have designed, and had installed, new disconnects with short circuit protection upstream from existing fire pump services. They have not been questioned by the AHJ.
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 43 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals