#213944 - 09/10/14 06:20 PM Cord drops in warehouse  
kit  Offline
New Member
Joined: Sep 2014
Posts: 2
ky
I am working in a 100,000 sq ft warehouse, it is 36' to the bar joists. It has racking throughout the warehouse with shipping and receiving areas. There are workstations with desks, computors, copiers and etc throughout the warehouse in various locations. They need power and data to these desks. I want to know how to get power down from the bar joists above to the work stations that OSHA and the NEC will approve. Can I drop from the bar joists at 36' with a cord and put a box with a plug on it? I wold use wir grip (kellems) on both ends of the cord and boxes with hubs.


2017 / 2014 NEC & Related Books and Study Guides

#213945 - 09/10/14 07:27 PM Re: Cord drops in warehouse [Re: kit]  
ghost307  Offline
Member
Joined: May 2005
Posts: 900
Chicago Illinois USA
Most of the installation that I have seen for this involve putting the desks against a wall or column and using that as a conduit route from the roof trusses down to the furniture.
A free-hanging (and free-swinging) cord would likely not be looked upon kindly by the AHJ.


Ghost307

#213946 - 09/10/14 08:50 PM Re: Cord drops in warehouse [Re: kit]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,060
Estero,Fl,usa
Pendant cords are legal but you need the right strain relieving hardware, hard service cord and generally twist lock receptacles.
If they are not moving these around, you could come floor to ceiling with strut and strap EMT to that. Hang a box there.


Greg Fretwell

#213947 - 09/10/14 10:30 PM Re: Cord drops in warehouse [Re: kit]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,803
Brick, NJ USA
High cube warehouses have EMT secured to the rack uprights, protected from any physical damage. The furniture is placed where the outlets are located. EMT for data also.

NEC 400.8, and 400.7 is where to look.

I accept, depending on the individual job, a twistlock receptacle at the bar joists, a kellems, and a TL male cap with a compliant device on the 'user' end of the cord. (Basically an 'extension cord)

Cord drops are an item that has been debated for a long, long time. IMHO, talk to your local AHJ, before you start.



John

#213950 - 09/11/14 09:16 AM Re: Cord drops in warehouse [Re: kit]  
kit  Offline
New Member
Joined: Sep 2014
Posts: 2
ky
Thanks for the help, looks like there is a lot of work to do to straighten up what they have.



Member Spotlight
sparky66wv
sparky66wv
West Virginia
Posts: 2,236
Joined: November 2000
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 15 (0.003s) Memory: 0.7668 MB (Peak: 0.9074 MB) Zlib enabled. Server Time: 2017-03-30 04:46:55 UTC