The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
breaker meltdown
by crselectric
09/24/16 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 15
sparky 9
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 292 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#213944 - 09/10/14 03:20 PM Cord drops in warehouse
kit Offline
New Member

Registered: 09/10/14
Posts: 2
Loc: ky
I am working in a 100,000 sq ft warehouse, it is 36' to the bar joists. It has racking throughout the warehouse with shipping and receiving areas. There are workstations with desks, computors, copiers and etc throughout the warehouse in various locations. They need power and data to these desks. I want to know how to get power down from the bar joists above to the work stations that OSHA and the NEC will approve. Can I drop from the bar joists at 36' with a cord and put a box with a plug on it? I wold use wir grip (kellems) on both ends of the cord and boxes with hubs.

Top
2014 / 2011 NEC & Related Books and Study Guides
#213945 - 09/10/14 04:27 PM Re: Cord drops in warehouse [Re: kit]
ghost307 Offline
Member

Registered: 05/09/05
Posts: 876
Loc: Chicago Illinois USA
Most of the installation that I have seen for this involve putting the desks against a wall or column and using that as a conduit route from the roof trusses down to the furniture.
A free-hanging (and free-swinging) cord would likely not be looked upon kindly by the AHJ.
_________________________
Ghost307

Top
#213946 - 09/10/14 05:50 PM Re: Cord drops in warehouse [Re: kit]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
Pendant cords are legal but you need the right strain relieving hardware, hard service cord and generally twist lock receptacles.
If they are not moving these around, you could come floor to ceiling with strut and strap EMT to that. Hang a box there.
_________________________
Greg Fretwell

Top
#213947 - 09/10/14 07:30 PM Re: Cord drops in warehouse [Re: kit]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
High cube warehouses have EMT secured to the rack uprights, protected from any physical damage. The furniture is placed where the outlets are located. EMT for data also.

NEC 400.8, and 400.7 is where to look.

I accept, depending on the individual job, a twistlock receptacle at the bar joists, a kellems, and a TL male cap with a compliant device on the 'user' end of the cord. (Basically an 'extension cord)

Cord drops are an item that has been debated for a long, long time. IMHO, talk to your local AHJ, before you start.
_________________________
John

Top
#213950 - 09/11/14 06:16 AM Re: Cord drops in warehouse [Re: kit]
kit Offline
New Member

Registered: 09/10/14
Posts: 2
Loc: ky
Thanks for the help, looks like there is a lot of work to do to straighten up what they have.