The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Yesterday at 09:52 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 08:24 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
HotLine1 6
renosteinke 6
ghost307 5
Potseal 4
Who's Online
2 registered (Tjia1981, sparkyinak), 236 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#213944 - 09/10/14 03:20 PM Cord drops in warehouse
kit Offline
New Member

Registered: 09/10/14
Posts: 2
Loc: ky
I am working in a 100,000 sq ft warehouse, it is 36' to the bar joists. It has racking throughout the warehouse with shipping and receiving areas. There are workstations with desks, computors, copiers and etc throughout the warehouse in various locations. They need power and data to these desks. I want to know how to get power down from the bar joists above to the work stations that OSHA and the NEC will approve. Can I drop from the bar joists at 36' with a cord and put a box with a plug on it? I wold use wir grip (kellems) on both ends of the cord and boxes with hubs.

2014 / 2011 NEC & Related Books and Study Guides
#213945 - 09/10/14 04:27 PM Re: Cord drops in warehouse [Re: kit]
ghost307 Offline

Registered: 05/09/05
Posts: 881
Loc: Chicago Illinois USA
Most of the installation that I have seen for this involve putting the desks against a wall or column and using that as a conduit route from the roof trusses down to the furniture.
A free-hanging (and free-swinging) cord would likely not be looked upon kindly by the AHJ.

#213946 - 09/10/14 05:50 PM Re: Cord drops in warehouse [Re: kit]
gfretwell Offline


Registered: 07/20/04
Posts: 9024
Loc: Estero,Fl,usa
Pendant cords are legal but you need the right strain relieving hardware, hard service cord and generally twist lock receptacles.
If they are not moving these around, you could come floor to ceiling with strut and strap EMT to that. Hang a box there.
Greg Fretwell

#213947 - 09/10/14 07:30 PM Re: Cord drops in warehouse [Re: kit]
HotLine1 Offline


Registered: 04/03/02
Posts: 6791
Loc: Brick, NJ USA
High cube warehouses have EMT secured to the rack uprights, protected from any physical damage. The furniture is placed where the outlets are located. EMT for data also.

NEC 400.8, and 400.7 is where to look.

I accept, depending on the individual job, a twistlock receptacle at the bar joists, a kellems, and a TL male cap with a compliant device on the 'user' end of the cord. (Basically an 'extension cord)

Cord drops are an item that has been debated for a long, long time. IMHO, talk to your local AHJ, before you start.

#213950 - 09/11/14 06:16 AM Re: Cord drops in warehouse [Re: kit]
kit Offline
New Member

Registered: 09/10/14
Posts: 2
Loc: ky
Thanks for the help, looks like there is a lot of work to do to straighten up what they have.