The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Massive power outage South Australia
by Meadow
09/29/16 06:46 AM
short circuit??
by Meadow
09/29/16 06:43 AM
Norwegian power?
by Meadow
09/29/16 06:36 AM
breaker meltdown
by sparky
09/27/16 07:30 PM
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 13
sparky 10
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 98 Guests and 3 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#213917 - 09/06/14 08:35 PM 4800v. Directional Boring
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Here's the deal (Ernie pay attention) can a contractor install a 4800v. feeder using directional boring run 1000 feet and not install a "Warning ribbon" 12" above the conductors? See (NEC 300.50).

Second question, if he needs the "warning ribbon" how does he install it?

Note- this is a feeder not Service conductors.
_________________________
George Little

Top
2014 / 2011 NEC & Related Books and Study Guides
#213918 - 09/07/14 12:27 PM Re: 4800v. Directional Boring [Re: George Little]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
George:
The only reference to 'directional boring' that I can find within the '11 NEC is 300.5 (k).

Neither relates directly toyour question.

Boring is something I have not come upon here.

There is no reference within 'over 600 volts' regarding boring that I find.

All the high voltage I come upon is in duct banks & concrete encased.
_________________________
John

Top
#213922 - 09/07/14 06:54 PM Re: 4800v. Directional Boring [Re: George Little]
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Maybe the question should be: Can you directional bore customer owned conductors over 600v.
_________________________
George Little

Top
#213923 - 09/08/14 01:05 AM Re: 4800v. Directional Boring [Re: George Little]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
I don't know about customer owed but the utilities do it all the time around here and I am sure they are not boring another hole for a warning ribbon.
They bored a HV line behind my house that I am betting was over 100kv. The existing on the poles is (2)48kv and 250kv.
_________________________
Greg Fretwell

Top
#213924 - 09/08/14 09:21 AM Re: 4800v. Directional Boring [Re: George Little]
mbhydro Offline
Member

Registered: 02/21/03
Posts: 340
Loc: Winnipeg MB Canada
Would boring in the orange HPDE pipe and then pulling the cable in be more acceptable?

Top
#213929 - 09/08/14 07:36 PM Re: 4800v. Directional Boring [Re: George Little]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
George:
Talking to two HV guys today, neither has done any directional boring installs.

I'm curious to see if Scott35 has any comments from the 'shaky side'!!

Last two, and one upcoming (13.2KV) at the college are duct banks (4x5" PVC) and concrete encasement. (Red concrete), per specs.
_________________________
John

Top
#213941 - 09/10/14 07:42 AM Re: 4800v. Directional Boring [Re: George Little]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
George
Done all the time. Why DB if your gonna dig up the street or sidewalk to put ribbon.
Yoopersup

If we install HDPE in a open trench (which we do sometimes),
Ribbon is installed then.


Edited by Yoopersup (09/10/14 07:44 AM)
Edit Reason: Add

Top
#213942 - 09/10/14 08:07 AM Re: 4800v. Directional Boring [Re: George Little]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
George
Conductors marked with a rated temperature higher than that of the raceway can be used when the conductors are operated within the raceway temperature rating.

One application of 353.10(6) is the use of 105C-rated medium voltage cables, Type MV, where the cable ampacity at
the 105C rating is reduced to the cable ampacity at 75C or 90C to match the listed operating temperature rating of HDPE (75C or 90C).
Direct bury power cable systems are designed for long life, use of HDPE conduit to encase and protect the power cable from rock impingement is gaining favor as it allows for quick and easy repairs without excavation of the cable. HDPE conduit and innerduct is used to carry low 600V-transformer to end user) and medium (<69kV-substation to transformer) voltage power lines.

Yoopersup

Top
#213948 - 09/10/14 09:31 PM Re: 4800v. Directional Boring [Re: George Little]
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Thanks Ernie, I knew you dealt with this type of installation on a regular basis and would have a good answer.

See ya in Frankenmuth.
_________________________
George Little

Top