#213853 - 08/16/14 01:27 PM Can't find code reference. Help
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
I seem to remember that in the NEC it said that the grounded conductor (neutral) had to originate from the same panel as the ungrounded conductor. Has that been removed, or am I just wrong? I'm thinking there was an issue with the "Gentran" box used with portable generators. or possibly this 8 circuit panel that includes the transfer switch made by Generac. Thanks in advance.
_________________________
George Little
Top
2017 / 2014 NEC & Related Books and Study Guides
#213854 - 08/16/14 05:58 PM Re: Can't find code reference. Help [Re: George Little]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
As far as I know, the grounded conductor originates in the service disconnect enclosure where the main bonding jumper lands. Beyond that it just needs to be run in the same cable or raceway as the ungrounded conductors.

Maybe I don't understand the question.
_________________________
Greg Fretwell
Top
#213855 - 08/16/14 06:33 PM Re: Can't find code reference. Help [Re: George Little]
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
I guess I didn't explain it very well. I'm talking about a situation where we have the ungrounded conductors originating in one panel and the grounded conductors being in another panel like you could end up with using a generator and a transfer switch.

300.3(B) kinda covers it but I was thinking of the situation where the neutrals are coming from a different source.
_________________________
George Little
Top
#213856 - 08/16/14 07:45 PM Re: Can't find code reference. Help [Re: George Little]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
Yup that was where I was going.
_________________________
Greg Fretwell
Top
#213857 - 08/16/14 07:48 PM Re: Can't find code reference. Help [Re: George Little]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
Where is the neutral coming from and how can they do that without violating 300.3
_________________________
Greg Fretwell
Top
#213858 - 08/17/14 12:03 PM Re: Can't find code reference. Help [Re: George Little]
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
Wouldn't 300.3(B)(4) be similar in practice to the way a gen-tran transfer switch is installed?

Top
#213859 - 08/17/14 12:08 PM Re: Can't find code reference. Help [Re: George Little]
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
With those gen-tran switches and all the AFCI breakers required...you can't use them and keep the AFCI protection while on generator.
Top
#213860 - 08/17/14 01:58 PM Re: Can't find code reference. Help [Re: George Little]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
Looking at the GenTran installation guide, it does appear that there is a neutral bus in the GenTran and they talk about installing the required GFCI/AFCI breakers in the GenTran.
http://gentran.net/assets/pdfs/EncoreInstall.pdf

I also saw another smaller GenTran that looks like it uses plug fuses. That would be troubling on a new installation. There does not seem to be any provision for xFCI

https://gentran.net/assets/pdfs/oldinstall.pdf
_________________________
Greg Fretwell
Top
#213861 - 08/17/14 02:43 PM Re: Can't find code reference. Help [Re: George Little]
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
It is the smaller gen-tran switch that is most popular. It is sold in home stores also. This is the one without neutral provisions.
Top
#213862 - 08/17/14 10:03 PM Re: Can't find code reference. Help [Re: George Little]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
The Encore is the one I see listed at my local Home Depot.

If they have one that will not accommodate xFCI breakers and does not have a neutral bus, I would call it a violation, on a couple of counts.
Even if they could make the case that none of the circuits served required GFCI or AFCI, I would still have trouble with the edison base fuse holders, even if they do have push button breakers in them.
(like the second one in my post above)
_________________________
Greg Fretwell
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (Admin), 89 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/01/07
Posts: 62

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals