The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 175 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#213825 - 08/02/14 08:48 AM Label or the manual
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
An interesting issue came up over on one of the Usenet groups

There is a Sea Breeze mini split air conditioner that has an installation manual that says it should be connected with 6 gauge copper. The label says "minimum circuit ampacity" is 26 amps. So who do you believe?
The breaker size is 50a.
http://www.irproducts.biz/documents/SB-NewMultiZone.pdf
_________________________
Greg Fretwell

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#213826 - 08/02/14 09:19 AM Re: Label or the manual [Re: gfretwell]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Greg:
Well, in the real world....the nameplate wins. I would rarely see an install manual; I would ask for it if I had a question, and hope the HO had it.

They may have sized the branch circuit based on the OCP?
_________________________
John

Top
#213827 - 08/02/14 10:11 AM Re: Label or the manual [Re: gfretwell]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Quote:
They may have sized the branch circuit based on the OCP?



Clearly that is what happened. ... in the 60c column
_________________________
Greg Fretwell

Top
#213829 - 08/02/14 10:57 PM Re: Label or the manual [Re: gfretwell]
Scott35 Offline

Broom Pusher and
Member

Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
Curiosity query...

What was the Intensity level of Flames emitted (by the Usenet Members), when the reply Message stating:
"#10 THW Cu. is Adequate and Compliant"
was posted to the Thread???
laugh yay rolleyes bash

--Scott (EE)
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Top
#213830 - 08/02/14 11:04 PM Re: Label or the manual [Re: gfretwell]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
One guy in particular still will not let it go.

They are off on a "continuous load" side track now.
I tried to explain that motor circuits already have the 125% of FLA requirement and this would be part of the minimum ampacity calculation.

I explained I would trust the engineer who did that calculation more than a tech writer who might not have English as his first language.
_________________________
Greg Fretwell

Top
#213844 - 08/11/14 05:28 PM Re: Label or the manual [Re: gfretwell]
anothermarty Offline
New Member

Registered: 02/10/06
Posts: 3
Loc: MA
Label for outdoor unit only... all the inside coils grab power from the outdoor unit.

Now why its ok to use 14/3 or4 between inside and outside can start another argument smile

Top
#213845 - 08/11/14 07:54 PM Re: Label or the manual [Re: gfretwell]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Correct me if this is wrong....
The inside unit (fan coil) is fed from the outside unit (condenser) and there is factory OCP for the fan coil feed within the condenser.

Most of the units I have seen have 'factory' wiring from the Cu to the FC.
_________________________
John

Top
#213846 - 08/11/14 10:15 PM Re: Label or the manual [Re: gfretwell]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
I have 2 of these mini splits and one the inside units runs on low voltage that could be run with bell wire Spec'ed as thermostat cable. It is a very small load (a little fan and an electronic board).
The other uses line voltage but just at a few amps.
_________________________
Greg Fretwell

Top
#213847 - 08/11/14 11:06 PM Re: Label or the manual [Re: gfretwell]
anothermarty Offline
New Member

Registered: 02/10/06
Posts: 3
Loc: MA
A few amps x 4-5 inside line voltage coils adds up Read the specs 3.5x up to 5 so about 17 amps total inside plus 26 out 50 amps seems right

Top
#213848 - 08/12/14 10:01 AM Re: Label or the manual [Re: gfretwell]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
The conductors going to each inside unit only carry the current to that unit. That is why they can be #14.
As for the outside unit, that is specified on the label and you have to trust the engineer who computed it.
_________________________
Greg Fretwell

Top