#213535 - 05/29/14 05:25 PM UV heaters
schenimann Offline
Member
Registered: 02/18/08
Posts: 193
Loc: Western North Carolina
I have a job next week wiring a UV heater for a printing press. The heater is rated at 80 amps. I have never messed with these before. Do I need to upsize my breaker at all or does it get wired as it is rated? It is 240v 3ph. I don't do much 3ph work so this is a little out of my league.
Top
Work Gear for Electricians and the Trades
#213537 - 05/29/14 07:39 PM Re: UV heaters [Re: schenimann]
Tesla Offline
Member
Registered: 06/16/04
Posts: 1273
Loc: Sacramento, CA
For such exotic gear -- call their tech rep.

They may have pdf on the Web.

UV 'heaters' doesn't quite sound right. I strongly suspect that these are intermittent loads -- kind of like a Xerox machine.

BTW, 240VAC 3 phase is now an uncommon Service. They may have an associated 3 phase autoformer to boost 208Y120 up to the machine's requirement.

Is there any chance that this gadget is a component of their lithographic process?
_________________________
Tesla
Top
#213541 - 05/29/14 08:19 PM Re: UV heaters [Re: schenimann]
schenimann Offline
Member
Registered: 02/18/08
Posts: 193
Loc: Western North Carolina
UV heater is not quite right. It is actually UV bulbs for a drying process in their flexographic printing process. They currently have a 240VAC 3 phase service that we installed the 240VAC service about 7 years ago. I worked for my dad at the time so I'm not sure exactly why. Something with the POCO and available power in a rural residential area. He is haveing the equipment wired for this voltage.

I will call the tech rep. That is a good idea.
Top
#213543 - 05/29/14 09:42 PM Re: UV heaters [Re: schenimann]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
80a?
One single phase? 19.2KW element?
Or are there multiple elements spread across the phases?
Either way,
That is a heluva heater.

_________________________
Greg Fretwell
Top
#213555 - 06/01/14 09:26 AM Re: UV heaters [Re: schenimann]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
All the UV heaters (printing) I have come upon had a control panel that the feeder connected to, and the circuits feeding the individual lamp stations were 'factory' from the controller.

Ususl practice was to install the feeder to the MOCP on the controller nameplate.
_________________________
John
Top
#213557 - 06/01/14 05:12 PM Re: UV heaters [Re: schenimann]
WESTUPLACE Offline
Member
Registered: 03/29/04
Posts: 251
Loc: Kingwood, TX USA
I install and work on these all the time. They are also used in the screen printing business. Most rated at 80 amps will be served by a 100 amp service, but always go on the name plate rating. A disconnect should be installed at the machine. BTW 240v 3ph service is the norm here in Houston TX.
Top
#213572 - 06/04/14 08:28 AM Re: UV heaters [Re: schenimann]
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA
I have also dealt with UV Dryers, along with UV Ovens, in several Design-Build Projects (mostly on the "Design" side of the Projects).
The Lamps on a few "Older" UV Dryers were similar to the High Pressure Mercury HID Type Lamps used in 10KW Tanning Beds (Quartz Envelopes with fixed Conductor Leads).

As described by others in this Thread, refer to the Equipment's Nameplate FLA (or better yet, MCA), and design the Branch Circuit from the Load indicated per Nameplate.

Sidenote: Having a 240V 3 Phase Delta System available from the Utility, is so nice to have at the Service Equipment, when the Client's Equipment is rated 230-240VAC 3 Phase.
Otherwise, such Equipment is connected to an SDS (Transformer with 240V 3 Phase Delta Secondary), and that SDS is either Corner Grounded or Center-Tap Grounded. I prefer Center-Tap Grounding.

--Scott (EE)
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 55 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals