The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Today at 08:46 PM
International Wire Colour Codes
by Tjia1981
Yesterday at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 296 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#213535 - 05/29/14 05:25 PM UV heaters
schenimann Offline

Registered: 02/18/08
Posts: 194
Loc: Western North Carolina
I have a job next week wiring a UV heater for a printing press. The heater is rated at 80 amps. I have never messed with these before. Do I need to upsize my breaker at all or does it get wired as it is rated? It is 240v 3ph. I don't do much 3ph work so this is a little out of my league.

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#213537 - 05/29/14 07:39 PM Re: UV heaters [Re: schenimann]
Tesla Offline

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
For such exotic gear -- call their tech rep.

They may have pdf on the Web.

UV 'heaters' doesn't quite sound right. I strongly suspect that these are intermittent loads -- kind of like a Xerox machine.

BTW, 240VAC 3 phase is now an uncommon Service. They may have an associated 3 phase autoformer to boost 208Y120 up to the machine's requirement.

Is there any chance that this gadget is a component of their lithographic process?

#213541 - 05/29/14 08:19 PM Re: UV heaters [Re: schenimann]
schenimann Offline

Registered: 02/18/08
Posts: 194
Loc: Western North Carolina
UV heater is not quite right. It is actually UV bulbs for a drying process in their flexographic printing process. They currently have a 240VAC 3 phase service that we installed the 240VAC service about 7 years ago. I worked for my dad at the time so I'm not sure exactly why. Something with the POCO and available power in a rural residential area. He is haveing the equipment wired for this voltage.

I will call the tech rep. That is a good idea.

#213543 - 05/29/14 09:42 PM Re: UV heaters [Re: schenimann]
gfretwell Offline


Registered: 07/20/04
Posts: 9026
Loc: Estero,Fl,usa
One single phase? 19.2KW element?
Or are there multiple elements spread across the phases?
Either way,
That is a heluva heater.
Greg Fretwell

#213555 - 06/01/14 09:26 AM Re: UV heaters [Re: schenimann]
HotLine1 Offline


Registered: 04/03/02
Posts: 6792
Loc: Brick, NJ USA
All the UV heaters (printing) I have come upon had a control panel that the feeder connected to, and the circuits feeding the individual lamp stations were 'factory' from the controller.

Ususl practice was to install the feeder to the MOCP on the controller nameplate.

#213557 - 06/01/14 05:12 PM Re: UV heaters [Re: schenimann]

Registered: 03/29/04
Posts: 252
Loc: Kingwood, TX USA
I install and work on these all the time. They are also used in the screen printing business. Most rated at 80 amps will be served by a 100 amp service, but always go on the name plate rating. A disconnect should be installed at the machine. BTW 240v 3ph service is the norm here in Houston TX.

#213572 - 06/04/14 08:28 AM Re: UV heaters [Re: schenimann]
Scott35 Offline

Broom Pusher and

Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
I have also dealt with UV Dryers, along with UV Ovens, in several Design-Build Projects (mostly on the "Design" side of the Projects).
The Lamps on a few "Older" UV Dryers were similar to the High Pressure Mercury HID Type Lamps used in 10KW Tanning Beds (Quartz Envelopes with fixed Conductor Leads).

As described by others in this Thread, refer to the Equipment's Nameplate FLA (or better yet, MCA), and design the Branch Circuit from the Load indicated per Nameplate.

Sidenote: Having a 240V 3 Phase Delta System available from the Utility, is so nice to have at the Service Equipment, when the Client's Equipment is rated 230-240VAC 3 Phase.
Otherwise, such Equipment is connected to an SDS (Transformer with 240V 3 Phase Delta Secondary), and that SDS is either Corner Grounded or Center-Tap Grounded. I prefer Center-Tap Grounding.

--Scott (EE)
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!