#213394 - 04/21/14 12:40 PM 250.30(B) 3 & 250.30 (C)
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
Outdoor transformer Customer owned 13.8 Pri.
480/277 Secondary. Bond at Transformer as Required 250.30 (C)
sized by 250.66. 3 phases from Transformer Plus Ground to ist OCP. Can it be Bare Conductors (Parallel) & Must be sized by 250.66 as it's before OCP.
250.30 (B) 3.
Phase Conductors 6 sets of 750's .
750 x6 = 4500 x 12.5 % =5625.
Grounding conductor must be 600 mcm each conduit.
Your imput ?
Top
2017 / 2014 NEC & Related Books and Study Guides
#213418 - 04/25/14 11:39 AM Re: 250.30(B) 3 & 250.30 (C) [Re: Yoopersup]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
Questions are incase I didn't state them correctly?
Can a bare SSBJ be installed between the XO at the secondary of the transformer to the Switchgear with the phase conductors?? (there is no Neutral just 3 phases & SSBJ.

Second: system bonding jumper must be sized by 250.66????

Yoopers UP
see above post for details

Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (annemarie1), 53 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals