#213321 - 04/10/14 11:29 AM 13.8 volts in conduit
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
Question
13800 volt cables in conduit,
Two cables (Feeder in Feeder out).
Can they be run in same conduit if correct
sq inch of fill??
Conduit RSC but could be any type raceway.
Yoopersup
Top
2017 / 2014 NEC & Related Books and Study Guides
#213322 - 04/10/14 12:19 PM Re: 13.8 volts in conduit [Re: Yoopersup]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Art 215 seems not to address this in the over 600v sections.

Sounds like a design issue with the info you provided. OCP, conductor sizes, what the 'in' & 'out' are, etc., and time to research may all be needed. Derating may be required.

Scott35 what say you??
_________________________
John
Top
#213323 - 04/10/14 03:07 PM Re: 13.8 volts in conduit [Re: Yoopersup]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
I am sure you are be derating this to 80% (4-6 conductors) but I can't think of a code reason why it would be prohibited.
If one set was service conductors it is a problem.
_________________________
Greg Fretwell
Top
#213324 - 04/10/14 03:11 PM Re: 13.8 volts in conduit [Re: Yoopersup]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
310.60 Conductors Rated 2001 to 35,000 Volts.
Derateing HV conductors.
I don't think their done the same as under 600 volts.
Top
#213325 - 04/10/14 04:38 PM Re: 13.8 volts in conduit [Re: Yoopersup]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
Watts is watts and that means heat. I bet if you run that formula you will end up being in the same place.

I suppose you should just demand the calculation because there is not a table for 4-6 conductors.
I am just a "pump and pulley" guy and that sort of math makes my head hurt. wink
_________________________
Greg Fretwell
Top
#213326 - 04/10/14 04:55 PM Re: 13.8 volts in conduit [Re: Yoopersup]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
Can you even put more then 3 Phase conductors + ground or Neutral in a single conduit?? I've never seen it Done???
HV ductbanks are derated by the number of conduits in the Ductbank not wires in the conduit.
Figure 310.60 Page 342 NFPA Code handbook.
70-159 NEC 2011
Top
#213328 - 04/10/14 07:46 PM Re: 13.8 volts in conduit [Re: Yoopersup]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
I am not sure why it would be prohibited but I think you pointed out why it is not attractive.

It sounds like you need engineering to determine ampacity.
_________________________
Greg Fretwell
Top
#213329 - 04/10/14 09:24 PM Re: 13.8 volts in conduit [Re: Yoopersup]
Tesla Offline
Member
Registered: 06/16/04
Posts: 1273
Loc: Sacramento, CA
Purely hypothetical brain teasers are unworthy.

The better question is: At such power levels and cable sizes, when would it ever be economic to do so?

The swift answer is: Never.
_________________________
Tesla
Top
#213330 - 04/11/14 07:44 AM Re: 13.8 volts in conduit [Re: Yoopersup]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
Tesla
Sorry not Hypothetical. Read Field problem.
Three 13.8 Switches single feed, Jumpers in between each (line side).
Load off each switch proposed to run thur same nipple as feed to switch! I don't make this stuff up I run into it!
Power calculations, Fill ect no problem.
Yoopersup

Nuff said.
Top
#213331 - 04/11/14 08:39 AM Re: 13.8 volts in conduit [Re: Yoopersup]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
Tesla
Sent you info on the E-mail you listed on here.
Codemanec
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 50 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals