#213180 - 03/27/14 05:43 PM Bare Copper In Raceway
watersparkfalls Offline
Member
Registered: 03/08/05
Posts: 212
Loc: Washington...Not DC
I went to look at a job, where some copper thieves stole the parking lot light control wires, from a church none the less.
I discovered the ground wire pulled with the home run is bare copper, which I thought was against code in a raceway. Am I right? Or was this another myth I believed in? Also what do you think about split bolting the 3 control wires and heat shrinking them in each hand hole? $50 a pop for the resin kits seems kinda pricing, when split bolts/heat shrink work just fine.

Thanks, H20


Edited by watersparkfalls (03/27/14 05:45 PM)
Top
2017 / 2014 NEC & Related Books and Study Guides
#213181 - 03/27/14 06:47 PM Re: Bare Copper In Raceway [Re: watersparkfalls]
Tesla Offline
Member
Registered: 06/16/04
Posts: 1273
Loc: Sacramento, CA
I don't work the traffic and signals market...

But the last NEC/ IBEW job I saw used bare #10 solid as the grounding conductor inside PVC for street illumination. It appeared that they used 1 1/4" as their minimum conduit size.

I was kind of jealous, they had an entire 20-foot double axle trailer dedicated to holding their conductor selections. I could never get such a rig to roll around our big box slabs.

That's the only contractor I can recall using bare grounding conductors -- excluding bare solid grounding electrode conductors.
_________________________
Tesla
Top
#213182 - 03/27/14 06:54 PM Re: Bare Copper In Raceway [Re: watersparkfalls]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
The only restriction I know that might affect that is that 8ga or larger solid is not allowed in a raceway.
The only exception I can think of is a GEC.

Quote:
310.3 Stranded Conductors.
Where installed in raceways, conductors of size 8 AWG and larger shall be stranded.
Exception: As permitted or required elsewhere in this Code.
_________________________
Greg Fretwell
Top
#213185 - 03/28/14 07:54 AM Re: Bare Copper In Raceway [Re: watersparkfalls]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6775
Loc: Brick, NJ USA
H2o:
No issue with the bare to my knowledge as Greg said.

Now, the split bolt issue. Do you mean 3 control conductors, or you have to put 3 into a split bolt?
Most, if not all split bolts are only listed/labeled (your choice) for two (2) conductors. ie; run/tap. Your AHJ may have an issue with 3 conductors.



_________________________
John
Top
#213190 - 03/28/14 12:19 PM Re: Bare Copper In Raceway [Re: watersparkfalls]
watersparkfalls Offline
Member
Registered: 03/08/05
Posts: 212
Loc: Washington...Not DC
HotLine I was going to put all 3 control wires in the split bolt, NSI industries claim to have a listed split bolt for 3 copper wires. However I am leaning towards Ideals blue weatherproof wirenuts, they are rated for wet locations and my connections are in a hand hole, so might truly be the safest and cost effective way to reconnect lights. Need to secure hand holes from future thefts any thoughts on how to? Was thinking drilling and tapping, but that diamond plate is thick.

Not sure where I got it in my head "no bare in raceway" however I will double check my WAC(Washington Administrative Code)book, however if previous installer was signed off, must be fine.

Thanks,
H20
Top
#213191 - 03/28/14 12:50 PM Re: Bare Copper In Raceway [Re: watersparkfalls]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6775
Loc: Brick, NJ USA
The Ideal big blues sound like a plan.
_________________________
John
Top
#213204 - 03/29/14 12:02 PM Re: Bare Copper In Raceway [Re: watersparkfalls]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 1307
Loc: Alaska
Bare copper ground in a conduit is not a code issue spec issue perhaps but not a code issue.

As for the split bolts/resin question. That depends on the "engineer" of the project. If done right, split bolt/resin is definently bullet proof for a long tern installation. Way better then wire nuts given their location. If no rework or add to later is not in the cards, bullet proof is a definent plus if the customers are willing to pay for it.
_________________________
"Live Awesome!" - Kevin Carosa
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 44 Guests and 20 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals