The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
2 registered (LongRunner, Tjia1981), 178 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#213122 - 03/22/14 02:56 PM Emergency light exception
sparkync Offline
Member

Registered: 10/17/02
Posts: 811
Loc: NC
In the project I am doing, I have 4 circuits feeding overhead florescent lighting on 4 separate switches. The architect has drawn in a 16 recess gimble type emergency lights. Code reference 700.12 (F)under exception #1,says that I can run a separate circuit for the "unit lighting" instead of having to be on the same circuit if the qualifications are met. It says the minimum is 3 and I have 4 so as far as I can see I meet these qualifications. And it is in a separate and uninterrrupted area (no walls)and all lights are coming from the same panelboard, and I can put a lock on the breaker that controls the emergency lighting circuit. I was about to miss this exception and wire the related emergency lights ahead of each switched circuit. Am I thinking right? Thanks

Top
2014 / 2011 NEC & Related Books and Study Guides
#213137 - 03/22/14 07:48 PM Re: Emergency light exception [Re: sparkync]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Yep U are.

Top
#213166 - 03/26/14 10:01 AM Re: Emergency light exception [Re: sparkync]
sparkync Offline
Member

Registered: 10/17/02
Posts: 811
Loc: NC
Unfortunately for the owner, the electrical engineer has chose to ignore the "exception", and is requiring that each set of emergency lights in the area of each circuit be tied in ahead of the switch in that circuit. I know that the NEC is only a minimum. I tried:(