The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
breaker meltdown
by sparky
09/27/16 07:30 PM
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 13
sparky 10
sparky66wv 8
gfretwell 8
Vlado 6
Who's Online
0 registered (), 240 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#213122 - 03/22/14 02:56 PM Emergency light exception
sparkync Offline
Member

Registered: 10/17/02
Posts: 811
Loc: NC
In the project I am doing, I have 4 circuits feeding overhead florescent lighting on 4 separate switches. The architect has drawn in a 16 recess gimble type emergency lights. Code reference 700.12 (F)under exception #1,says that I can run a separate circuit for the "unit lighting" instead of having to be on the same circuit if the qualifications are met. It says the minimum is 3 and I have 4 so as far as I can see I meet these qualifications. And it is in a separate and uninterrrupted area (no walls)and all lights are coming from the same panelboard, and I can put a lock on the breaker that controls the emergency lighting circuit. I was about to miss this exception and wire the related emergency lights ahead of each switched circuit. Am I thinking right? Thanks

Top
2014 / 2011 NEC & Related Books and Study Guides
#213137 - 03/22/14 07:48 PM Re: Emergency light exception [Re: sparkync]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Yep U are.

Top
#213166 - 03/26/14 10:01 AM Re: Emergency light exception [Re: sparkync]
sparkync Offline
Member

Registered: 10/17/02
Posts: 811
Loc: NC
Unfortunately for the owner, the electrical engineer has chose to ignore the "exception", and is requiring that each set of emergency lights in the area of each circuit be tied in ahead of the switch in that circuit. I know that the NEC is only a minimum. I tried:(