#212297 - 12/29/13 11:15 AM Pull box size
zapped2012 Offline
New Member
Registered: 12/29/13
Posts: 2
Loc: United States New Jersey
what size pull box would I need if I have 3 4 inch conduits on one side and going out the back with 3 4 inch condits all having 4 600 mcms in them with a removable cover..
I came up with a box of 36x36x8 please help??
Top
2017 / 2014 NEC & Related Books and Study Guides
#212301 - 12/29/13 12:14 PM Re: Pull box size [Re: zapped2012]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 1307
Loc: Alaska
Good morning and welcome to the board. Unfortunately my code book is at the office but if you have a code book handy, it will be in chapter 3 under pull boxes
_________________________
"Live Awesome!" - Kevin Carosa
Top
#212304 - 12/29/13 12:19 PM Re: Pull box size [Re: zapped2012]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
First...Welcome to ECN from one of the "Jersey Guys"!!

Based on 314 and reference back to 312.6(a) for the removable cover, you got it.

That said, think about the actual layout you intend. The 8" depth may be a battle with the 600s, as the 36" side to side space. Keep in mind the result of the 314/312 calcs is the 'code minimum', and not the "ultimate" answer.

You may decide on a 40" or 48" x 12" box.....think ease of install, possible labor savings, and 'for sure' code compliance.
_________________________
John
Top
#212317 - 12/29/13 08:56 PM Re: Pull box size [Re: zapped2012]
Tesla Offline
Member
Registered: 06/16/04
Posts: 1273
Loc: Sacramento, CA
You make this sound like it's a test question.

36" is w a a a y too long if you're going in one face -- and plunging out the back side. "and going out the back"

600 kCMIL is brutally stiff -- even in aluminum -- so I could never recommend going with 8" as a depth.

You are not providing ANY of the circumstances that would dominate my own can sizing -- which is never predicated upon the NEC minimums. (I never, ever, attempt to squeeze (feeder) conductors into spaces so tight.)

Lowest cost means that the actual installation goes off without a hitch. That will not happen with NEC minimums. Tight space takes extra time... sometimes amazing amounts of extra time.

The NEC permits 9 #12 THHN in 1/2" EMT. Only a fool would design to such a scheme. Five #12 is the maximum that one would want to run in 1/2" EMT. Nine #12 -- going through four full nineties -- may require use of a power tugger. Yes, it can get that bad. Pulls like that cause the back injuries so common to electricians.





_________________________
Tesla
Top
#212326 - 12/30/13 12:31 PM Re: Pull box size [Re: zapped2012]
zapped2012 Offline
New Member
Registered: 12/29/13
Posts: 2
Loc: United States New Jersey
Just need to see if i was right not a test what size would you use Thanks for your help
Top
#212460 - 01/09/14 09:19 AM Re: Pull box size [Re: zapped2012]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
2011 NEC 600 Volts & under . 314.28 A (2).
6 x 4 =24 + 8 = 32 inch by 32 inch.
Depth see 314.28 A (2) exception .
That refers you to 312.6 (A). 70-175.
Wire per terminal 3.
600-700 wire per terminal = 12 inch Depth.

As Said by others . that is Minimum size!
If you ever pulled 600 mcm you would NOT use
minimum size.




Edited by Yoopersup (01/09/14 09:23 AM)
Top
#212465 - 01/09/14 01:04 PM Re: Pull box size [Re: zapped2012]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Yoop;
Truer words have not been spoken!!!
_________________________
John
Top

Member Spotlight
Member Since: 10/07/00
Posts: 3417
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals